 - NE Nebraska
 - EC
Well lets just say spoken words may be more obvious than written words on this one.It was humor.
The overhead power distribution system has its neutral grounded every alternate poles. Result? Stray leakage current throughout the land of this country.Compared to it, 100 W bulb ground current is infinitesimal, But it is allowed without seemingly any objection here!
An inaccurate generalisation.The overhead power distribution system has its neutral grounded every alternate poles.
At some voltages here the distribution is three wire delta. There is no neutral.
And just to compound the issue, not all distribution is overhead.
Then you have HVDC, 400kVdc in UK IIRC. DC and a neutral?
Quite possibly so.I think that Sahib may have been referring to the U.S. MGN system.
I have read in a number of sources that about 1/3 of the primary grounded conductor current on our MGN system flows via the earth.I think that Sahib may have been referring to the U.S. MGN system.
There is still a wire neutral that will be carrying most of the current as long as it is intact.
In practice, most bad results occur in the immediate vicinity of substations. Some POCOs seem to have a problem understanding how to correct or mitigate those problems.
Same in the USA especially in rural systems.The overhead power distribution system has its neutral grounded every alternate poles. Result? Stray leakage current throughout the land of this country.Compared to it, 100 W bulb ground current is infinitesimal, But it is allowed without seemingly any objection here!
Utilities are allowed and do use earth as a conductor intentionally. On MGM conductor it saves the utilities millions of dollars as the earth return has far lower impedance than any conductor could possible be. In Alaska and some extremely remote area a system called SWER (Single Wire Earth Return) is used. A single high voltage line is connected to a transformer high side and a ground rod(s) driven used for the return.
Around here I believe you will find there is an electrode at nearly every pole or other structure that has over 600 volt lines attached to it, and most of the time even if under 600 volts.That would be incorrect. The MGN wire itself has a higher impedance than the earth return. The further away you get from the distribution sub, the majority of the return current is via Earth. The MGN is bonded to the pole butt ground every 4th pole. Once you get a mile or more away, the ground impedance is lower than the conductor.
Transmission on the other hand is Delta and no current flows in earth. HVDC transmission on the other hand does use Earth as a conductor.
I believe you as you will see that in dense populated area.Around here I believe you will find there is an electrode at nearly every pole or other structure that has over 600 volt lines attached to it, and most of the time even if under 600 volts.
It has been said on this site before but I can't remember who to credit, that the earth has a very low impedance, but it is hard to make a low impedance connection to earth. Well that is tue and part of the reason for all the confusion. The earth as a whole is an excellent conductor, but a resident or most businesses cannot get enough surface contact to use it. At low voltages under 600 volts is useless as a conductor.
An Electric utility on the other hand takes full advantage of earth for many reasons both economic and safety. They can so because they operate at very high voltages and build the generation plants and sub-stations with massive ground electrodes and test them yearly. I know because I was a sub-station engineer for the first ten years of my career. Transmission is all 3-phase Delta and really long line transmission is by-polar DC. Distribution is a mixed bag, Residential is Wye connected and thus a grounded circuit conductor must be used. POCO uses Earth as a parallel conductor to the MGN. Commercial can be either Delta or Wye, but residential by the nature of the beast is Wye. Rural is always Wye using MGN as it has to be.
Here is the USA we can belly ache all we want about our electrical architectural, but it cannot be changed. We made a huge mistake early on when we decided to use a unbalanced grounded system. It causes all kinds of problems but cannot be changed and we are stuck with it. It some ways at least on a house by house basis could be fixed somewhat by wiring everything 240, and that eliminates some of the problems on the user end, but will not address the distribution end. But where are you going to find all the gizmos in your house that can use 240?
Don't bet on that. The rapid rise and fall times of a fault represent a very high frequency for which there is no such thing as a low impedance.At least one virtue of the MGN SYSTEM, IMO: The resistance of a ground rod becomes very small, if not zero, once it is connected to the MGN. So if there is a phase to gound fault in an equipment connected with it, there is no dangerous touch potential for the duration the concerned OCPD takes to operate to clear the fault.