Service Entrance ATS mounted inside garage?

Status
Not open for further replies.

TimWA

Member
Backing up an entire residential main panel with a service-entrance rated ATS (ie. utility input to ATS directly from service meter load-side lugs), customers don't want ATS outside next to their front door, imagine that!
I imagine ATS mount inside garage is ok, just obeying the five-foot rule for unfused conductors? Anyone done this?
thanks,
-Tim
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Sounds fine as long as it complies with 230.70(A)(1). Although it may be a local limitation the NEC has no 5' limit.
 