Hello,
Just ran into this and want to get the forum opinion. We have a 2500KVA service transformer feeding 3 indivisual circuit breakers (ie. no main). The transformer secondary is 480VAC phase to phase and is wired directly to each of the 3 breakers via single conductors (lots of them). One of the breaker has an IC rating of 30KA while other two are 65KA. The 30KA rated breaker was made by a company call Federal Pioneer (this plant is quite old). I am not sure the SCA at the secondary is more than 30KA but more than likely. Has anyone heard of this company.
This is an issue and I am concern because of the IC rating. I was told the plant was "grandfather" due to its age and we don't need to worry about this. Something is amiss.
Please give your opinion.
Thanks.
FK19
Just ran into this and want to get the forum opinion. We have a 2500KVA service transformer feeding 3 indivisual circuit breakers (ie. no main). The transformer secondary is 480VAC phase to phase and is wired directly to each of the 3 breakers via single conductors (lots of them). One of the breaker has an IC rating of 30KA while other two are 65KA. The 30KA rated breaker was made by a company call Federal Pioneer (this plant is quite old). I am not sure the SCA at the secondary is more than 30KA but more than likely. Has anyone heard of this company.
This is an issue and I am concern because of the IC rating. I was told the plant was "grandfather" due to its age and we don't need to worry about this. Something is amiss.
Please give your opinion.
Thanks.