310.15(B)(16) Question

Status
Not open for further replies.
I recall somewhere in the code it indicates, for circuits less than 100A, the 60-degree C column should be used when selecting conductor size. For example, if using a 60A circuit, you must use #4 versus #6 as under the 75-degree C column.

Thanks for any replies.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
You are thinking of 110.14(C)(1). You are allowed to use the 75deg conductor below 100A if the equipment/terminations are rated for 75deg.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I agree with David in Post #2 but might add that the wiring method can play a role such as the requirement to terminate NM at the 60deg rating.
 

Smart $

Esteemed Member
Location
Ohio
I agree with David in Post #2 but might add that the wiring method can play a role such as the requirement to terminate NM at the 60deg rating.
While covered by David's statement, must elaborate that devices at the load end may only have 60?C rating.
 