1X4 TO CONCRETE CEILING

Status
Not open for further replies.

kwired

Electron manager
Location
NE Nebraska
Assuming by 1x4 you mean a 4 foot fluorescent luminaire that is only maximum 1 foot wide.

Probably in most cases wedge anchors or even tapcon type screws. Newer luminaires with electronic ballasts do not weigh that much at all and doesn't really take much to support them.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
We use some variation of this type of anchor exclusively for poured concrete.

05150_detail_DSC00480_logo-237x239.jpg


http://www.powers.com/pdfs/mechanical/06160.pdf
 