czars
Czars
- West Melbourne, FL
- Florida Certified Electrical Contractor
Has anyone had an experience with GE 2 pole breakers failing to trip when overloaded to 1.5+ times their rating for extended periods of time?
Possibly cold outdoor ambient temperatures?Has anyone had an experience with GE 2 pole breakers failing to trip when overloaded to 1.5+ times their rating for extended periods of time?
What type CB? What did the time-current trip curve show?Has anyone had an experience with GE 2 pole breakers failing to trip when overloaded to 1.5+ times their rating for extended periods of time?
Can you tell us what kind of time period you are referring to, as iceworm pointed out a properly functioning breaker can carry what some may think is surprising for fairly long time. The more the overload the faster it will trip though. Ambient temp at the breaker location will have some impact as well.Has anyone had an experience with GE 2 pole breakers failing to trip when overloaded to 1.5+ times their rating for extended periods of time?
How does that change the fact the breaker is doing what it is supposed to do - trip after 59 minutes? In a chilled data center the time would be even longer.Yep. Which is why one of the data centers I service requires every newly installed breaker to be tested.
... one of the data centers I service requires every newly installed breaker to be tested.
just curious - what spec do you test to?
ice
The OP simply said 'extended times'. I never said his breaker was working.I did not read enough information in the OP to come to a conclusion as to whether is was tripping correctly or incorrectly. How did you come to the conclusion that it's a fact that it was doing what it was supposed to do.
I don't expect to have to test new breakers to make sure they are good, but I don't usually buy GE unless there is an existing GE panel that I am running a new circuit to. I find it a little hard to believe their QC is that bad, but maybe it is. I do know the standards allow for a breaker to hold for time/amperage levels that some may think are kind of long/high, but remember these breakers are primarily protecting conductors, if you have certain equipment that you want more protection on then maybe some supplemental protection that meets the needs at that equipment is what is needed.Yep. Which is why one of the data centers I service requires every newly installed breaker to be tested.
Just curious - Do they check the instantaneous portion of the trip curve?... We send them to a breaker shop that does the testing. ... So I would be willing to bet that they use whatever GE specs on the THQB's.
... I do know the standards allow for a breaker to hold for time/amperage levels that some may think are kind of long/high, but remember these breakers are primarily protecting conductors, if you have certain equipment that you want more protection on then maybe some supplemental protection that meets the needs at that equipment is what is needed.
And at max interrupt rating rangesJust curious - Do they check the instantaneous portion of the trip curve?
ice
Maybe they should check fuses before using them as well![]()
Although, except for large feeders (say >1000A), the cable damage curve is rarely on the coordination curves. Still, one might say it could protect the couductors here.
Hey - I am keeping my tongue -- ahhh - fingers firmly in cheek. You are having too much fun.:roll:
ice
(emoticon substituted for invisible body language)