Breakers, and I REPEAT with EMPHASIS, should always be new, whether it be a 15 amp QO or a 6000amp switch gear draw out unit. You dont know the history or if its been improperly maintained. ...
Can't say I agree. I deal with plenty of stuff that is sufficiently old that I have to deal with a rebuilder. I do all I can to pick good ones. No generally not with 15A qob.
... If coordination, and reliability is less of a concern but ease of reseting is your like go with breakers. .
Don't agree. If coordination is an issue - CBs, electronic trips are likely mandatory. Mains, feeders, ansi damage points (xfm), cable damage curves, overload curves, motor starting curves. Get them pounded on to one T-C coordination curve and sometimes the contortions to get coordination is severely interesting. I recall one noted authority saying, "You can coordinate anything - It's just a matter of money."
.... One area breakers win hands down over fuses is 3 phase tripping and the ability to add shunt trip, ground fault protection ect. Fuses have the disadvantage of clearing only the faulted phase leaving the others energized in a possibly dangerous condition. But a fuse is nearly fail safe, and there is no such thing as one seizing up mechanically. ....
Yes,
Yes,
and Yes
...But doesnt the NEC and UL to some degree dictate the breaker must trip on a time current curve based on a thermal damage curve? .
Yes, as long as one sticks to standard stuff, GEthqb, SQDqo, molded case
...I know the conductors to motors may be under sized with breakers only be for instantaneous magnetic trip protection, and networks often rely on cables to burn a fault clear, but cant think of other times when conductors are heated beyond the damage curve.
Some curves are really strange:
Inverse (normal)
very inverse
extremely inverse (might be wrong on this one)
i^2t
i^4t
LSI
LS (no I)
LSIG
And sometimes these are what it takes to get bent around so one can get coordination.
However, my point was about things like unlimited outside taps. The OCPD at the end of the tap should protect against overload - all the electrons going in from the xfm end have to come out the ocpd end. Invariabily some one will ask so what happens if the xfm secondary overload in the middle and it doesn't show up at the ocpd. That is a backhoe attack. The protection against that is concrete and steel - not an ocpd.
Motor feeders, overload is set to 140%. CB is a T-M set to 250% fla. Cable protection looks pretty marginal. If this was any size, I'd be lookin for the cable damage curve.
The rest is design philosophy. I consider the motors and conductors are protected from overload by design. One protects the cables with concrete and steel. The CB is to put out the fire and save the structure - and generally can also protect a cable
Just some thoughts - I'm not stuck