Might not matter even if it is longer than 24", if you can apply the Exception to 310.15(A)(2).[/QUOTE

Still the OP is asking how many conductors-- 6 current carrying conductors -- the derate is dependant upon other factors

Sorry....Here is all of the info:

Raceway longer than 24"
3 phase 208, no nuetral
#10 THHN conductors

310.15(B)(16) 2014 code says conductor good for 40 amps.
6 CCC's derate to 80%
conductors now good for 32 amps, still fusable at 30 amps.

Any comments??? And thanks for the help.
 
Sorry....Here is all of the info:

Raceway longer than 24"
3 phase 208, no nuetral
#10 THHN conductors

310.15(B)(16) 2014 code says conductor good for 40 amps.
6 CCC's derate to 80%
conductors now good for 32 amps, still fusable at 30 amps.

Any comments??? And thanks for the help.

Short answer yes. :D
 