Might not matter even if it is longer than 24", if you can apply the Exception to 310.15(A)(2).Six, but if the raceway is 24" or less then it wouldn't matter.
Might not matter even if it is longer than 24", if you can apply the Exception to 310.15(A)(2).[/QUOTE
Still the OP is asking how many conductors-- 6 current carrying conductors -- the derate is dependant upon other factors
Might not matter even if it is longer than 24", if you can apply the Exception to 310.15(A)(2).[/QUOTE
Still the OP is asking how many conductors-- 6 current carrying conductors -- the derate is dependant upon other factors
Sorry....Here is all of the info:
Raceway longer than 24"
3 phase 208, no nuetral
#10 THHN conductors
310.15(B)(16) 2014 code says conductor good for 40 amps.
6 CCC's derate to 80%
conductors now good for 32 amps, still fusable at 30 amps.
Any comments??? And thanks for the help.
Sorry....Here is all of the info:
Raceway longer than 24"
3 phase 208, no nuetral
#10 THHN conductors
310.15(B)(16) 2014 code says conductor good for 40 amps.
6 CCC's derate to 80%
conductors now good for 32 amps, still fusable at 30 amps.
Any comments??? And thanks for the help.