Current Carrying Conductors

Status
Not open for further replies.

jazer

Senior Member
Location
Gibsonia, Pa
Might not matter even if it is longer than 24", if you can apply the Exception to 310.15(A)(2).[/QUOTE

Still the OP is asking how many conductors-- 6 current carrying conductors -- the derate is dependant upon other factors

Sorry....Here is all of the info:

Raceway longer than 24"
3 phase 208, no nuetral
#10 THHN conductors

310.15(B)(16) 2014 code says conductor good for 40 amps.
6 CCC's derate to 80%
conductors now good for 32 amps, still fusable at 30 amps.

Any comments??? And thanks for the help.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Sorry....Here is all of the info:

Raceway longer than 24"
3 phase 208, no nuetral
#10 THHN conductors

310.15(B)(16) 2014 code says conductor good for 40 amps.
6 CCC's derate to 80%
conductors now good for 32 amps, still fusable at 30 amps.

Any comments??? And thanks for the help.

Short answer yes. :D
 