Thanks for all the responses, it's nice to get different perspectives. Let me try to address some things. First, I know romex is a trademark and that UF is not the same. The title should have said UF.
Next, I tried to talk the powers that be into making the trunk cable long enough to get to the 12x12 box, but they tell me the cost is too much. Same for the "extension cable".
My plan is to terminate the trunk cables in a bell box with the UF, then run the UF to the 12x12. The micro inverters are Enphase 215's which equals 7.8A continuous. The temperature correction factor for this area will be .91, well within range of #12 UF.
I pride myself in being a craftsman, if something looks bad I'm the first to point it out. The last thing I want is to be called a hack, never have, never will. That being said, as long as the UF is secured properly, how is that worse than trunk cable or liquidtite or SO cable or MC? UF is sunlight resistant, rated for wet locations and like I said before, will be 99% shielded from the sun. I agree that zip ties are not the best way to go, but again, they won't be exposed to the sun.