joeyde44
- Chadds Ford, PA
I was called by a manufactures rep to trouble shoot a large existing snow melt installation. This is a large residential apartment/condo project with a multi story underground parking garage. There are (4) exterior concrete stairways with imbedded snow melt mats. There are (4) 200 Amp, 240 Volt panel boards for the branch circuit breakers and each panel is energized by the manufactures control devices using magnetic contactors.
After I replaced some failed sensors and reprogramed the controllers I did a manual test to check things out. I was not able to energize the panel boards because the feeders were protected by CH type GFR ground fault protectors and they were tripping the shunt trip feeder breakers. I disabled the ground fault detectors on the feeders in order to energize the panel boards and found that every single mat was working properly with no measurable ground fault current.
I need to give this customer a clean and safe working system. What next?