GlennG

Member
Location
Hicksville, NY
I just got a violation for not having an equipotential bond around a hot tub. I was under the impression it's not a requirement for that. The tub is on a small patio surface surrounded by grass, and no metal anywhere near the tub. We are on 2008 NEC. I read through 680 and can't seem to find where the equipotential bonding ring relates to hot tubs. Can someone please help me figure out what I am missing. Looking for code references. Thanks
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
680.42
A spa or hot tub installed outdoor must comply with part I & II of article 680 except as permitted in 680.42(a) and (b) that would otherwise apply to pools installed outdoors.
 

Ohms law

Senior Member
Location
Sioux Falls,SD
I just got a violation for not having an equipotential bond around a hot tub. I was under the impression it's not a requirement for that. The tub is on a small patio surface surrounded by grass, and no metal anywhere near the tub. We are on 2008 NEC. I read through 680 and can't seem to find where the equipotential bonding ring relates to hot tubs. Can someone please help me figure out what I am missing. Looking for code references. Thanks

What I read states you do not need equipotential bond around a hot tub according to 680.42(b)1,2,3,4. The only bonding I believe is required is the metal frame not including attachments for wooden staves, motor frame, light fixtures, etc.
Is it a listed as a self-contained spa? If it is look for a ANSI/UL 1563-2010, you should be good. Maybe I'm wrong or missing something. I have never ran into an issue with an inspector for this.
 

Ohms law

Senior Member
Location
Sioux Falls,SD
I just realized what i wrote: What I read states you do not need equipotential bond around a hot tub according to 680.42(b)1,2,3,4. The only bonding I believe is required is the metal frame, motor frame, light fixtures, etc. Not including fasteners for wooden staves, etc.
Is it a listed as a self-contained spa? If it is look for a ANSI/UL 1563-2010, you should be good. Maybe I'm wrong or missing something. I have never ran into an issue with an inspector for this.[/QUOTE]
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Equipotential bonding is required for a hot tub unless your area has accepted the TIA for tubs. That allows certain installs to not be required to have equipotential bonding.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Here is the TIA


Pursuant to Section 5 of the NFPA Regulations Governing Committee Projects, the National Fire Protection Association has issued
the following Tentative Interim Amendment to NFPA 70?, National Electrical Code?, 2011 edition. The TIA was processed by Panel
17 and the National Electrical Code Technical Correlating Committee, and was issued by the Standards Council on March 1, 2011,
with an effective date of March 21, 2011.

A Tentative Interim Amendment is tentative because it has not been processed through the entire standards-making procedures. It is
interim because it is effective only between editions of the standard. A TIA automatically becomes a proposal of the proponent for the
next edition of the standard; as such, it then is subject to all of the procedures of the standards-making process.

1. Revise 680.42(B) to read as follows:

680.42(B) Bonding. Bonding by metal-to-metal mounting on a common frame or base shall be permitted.

Exception No. 1: The metal bands or hoops used to secure wooden staves shall not be required to be bonded as required in 680.26.

Exception No. 2: A listed self-contained spa or hot tub that meets all of the following conditions shall not be required to have
equipotential bonding of perimeter surfaces installed as required in 680.26(B)(2):

(1) Is installed in accordance with manufacturer?s instructions on or above grade.
(2) The vertical measurement from all permanent perimeter surfaces within 30 horizontal inches (76 cm) of the spa to the top
rim of the spa is greater than 28 inches (71 cm).
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I agree with Edward ---680.42 for outdoor installs states to use parts I and II of art. 680. Part II has the equipotential bonding.
 

Ohms law

Senior Member
Location
Sioux Falls,SD
Equipotential bonding is required for a hot tub unless your area has accepted the TIA for tubs. That allows certain installs to not be required to have equipotential bonding.

I have never heard of TIA's until now. It would be nice if CEU instructors would bring this kind of stuff up to inform electricians.
 

kwired

Electron manager
Location
NE Nebraska
OP states that the 2008 NEC applies. The mentioned TIA only applies to 2011 AFAIK. If it applied to 2008 they likely would have changed the wording in 2011 to eliminate the need for the TIA.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
OP states that the 2008 NEC applies. The mentioned TIA only applies to 2011 AFAIK. If it applied to 2008 they likely would have changed the wording in 2011 to eliminate the need for the TIA.


A state can choose to amend the 2008 and accept the TIA if they choose but generally you are correct. NC has yet to adopt the TIA.
 

kwired

Electron manager
Location
NE Nebraska
A state can choose to amend the 2008 and accept the TIA if they choose but generally you are correct. NC has yet to adopt the TIA.
With an issue such as we have in this thread it gets more complicated when some are either on or about to switch to 2014, and others are still on 2008 or even earlier, especially when you have world wide participation in the forum.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
With an issue such as we have in this thread it gets more complicated when some are either on or about to switch to 2014, and others are still on 2008 or even earlier, especially when you have world wide participation in the forum.


I agree and it is even more complicated when local areas have their own amendments that are different from the state. This is why I stated IF your area has adopted the TIA. Probably unlikely that an area in the 2008 NEC will adopt the TIA.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
So under the 2014 I buy a hot tub, plop it on the patio and no EPG required. Do the same under the 2008 or 2011 (w/no TIA acceptance) and it requires the EPG?
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
What do you do if the tub is on a wooden deck 15' up from the ground?
The deck being more of a balcony, not much larger than the tub.
 