This is rather long and complicated but I would like to make sure I have calculated everything correctly. Sorry for it being so long but I wanted to include all of the info. Please advise.
The scenario.
We will be installing a 112.5 kva 480 to 120/208 3 ph transformer. The transformer will be supplying a 120/208 3 ph mlo panel.
The transformer will be fed from a breaker in a main distribution panel in a separate building. The wire run from the main distribution panel to the transformer is 650 feet in 3 inch schdl 40 pvc 36 inches deep.
1st- The ocpd at the main distribution panel for the primary side - 112,500VA / (480 ? 1.732) = 135.32A,
135.32 X 1.25 = 169.15A - The next standard size up OCPD = 175A
2nd- Sizing the primary side conductors.
175A ocpd = 2/0 AWG at 75 degrees c. according to Table 310.16
Voltage drop for 650 feet - 480x3% = 14.4 - I want my voltage drop to be under 14.4v
14.4v = (1.73 x K x Length x Amps) / kcmil
14.4 = (1.73 x 12.9 x 650 x 170) / Y
Y = 171251 circular mils = 4/0 wire
Now to size the ground I have to increase its size by the same percentage that I increased my current carrying conductors
2/0 wire = 133100 circular mils
4/0 wire = 211600 circular mils
133100/211600 = 63%
According to 250.122 my ground should be a #6 AWG = 26240 circular mils
26240/63% = 40,369 = #4 AWG
Mounted beside the transformer on the primary side there will be a disconnect. Does it need to be fused?
Now to size the secondary of the transformer.
112,500VA / (208 ? 1.732) = 312.27A
312.27 x 1.25 = 390 A
Next size up = 400 amps
After the transformer on the secondary side there will be a 400A fused disconnect.
After the disconnect will be the 120/208 400A rated panel
Wire size will be parallel runs of 4/0
More than 3 current carrying conductors requires reduction in allowable ampacity to 80%
4/0 at 90 degrees c = 260
260 x 0.8 = 216A
Two parallel feeds of 4/0 = 432A
Here is where I get a little mixed up.
The ground on the secondary, does it need to get sized according to the 400A disconnect or the conductors that it will be running with.
I believe it needs to be sized according to the disconnect so each conduit will need a #3 ground with the 4 4/0 conductors. Please correct me if I am wrong or if you find any mistakes in my calculations. Any advice would be appreciated.
Thanks in advance,
Keith
The scenario.
We will be installing a 112.5 kva 480 to 120/208 3 ph transformer. The transformer will be supplying a 120/208 3 ph mlo panel.
The transformer will be fed from a breaker in a main distribution panel in a separate building. The wire run from the main distribution panel to the transformer is 650 feet in 3 inch schdl 40 pvc 36 inches deep.
1st- The ocpd at the main distribution panel for the primary side - 112,500VA / (480 ? 1.732) = 135.32A,
135.32 X 1.25 = 169.15A - The next standard size up OCPD = 175A
2nd- Sizing the primary side conductors.
175A ocpd = 2/0 AWG at 75 degrees c. according to Table 310.16
Voltage drop for 650 feet - 480x3% = 14.4 - I want my voltage drop to be under 14.4v
14.4v = (1.73 x K x Length x Amps) / kcmil
14.4 = (1.73 x 12.9 x 650 x 170) / Y
Y = 171251 circular mils = 4/0 wire
Now to size the ground I have to increase its size by the same percentage that I increased my current carrying conductors
2/0 wire = 133100 circular mils
4/0 wire = 211600 circular mils
133100/211600 = 63%
According to 250.122 my ground should be a #6 AWG = 26240 circular mils
26240/63% = 40,369 = #4 AWG
Mounted beside the transformer on the primary side there will be a disconnect. Does it need to be fused?
Now to size the secondary of the transformer.
112,500VA / (208 ? 1.732) = 312.27A
312.27 x 1.25 = 390 A
Next size up = 400 amps
After the transformer on the secondary side there will be a 400A fused disconnect.
After the disconnect will be the 120/208 400A rated panel
Wire size will be parallel runs of 4/0
More than 3 current carrying conductors requires reduction in allowable ampacity to 80%
4/0 at 90 degrees c = 260
260 x 0.8 = 216A
Two parallel feeds of 4/0 = 432A
Here is where I get a little mixed up.
The ground on the secondary, does it need to get sized according to the 400A disconnect or the conductors that it will be running with.
I believe it needs to be sized according to the disconnect so each conduit will need a #3 ground with the 4 4/0 conductors. Please correct me if I am wrong or if you find any mistakes in my calculations. Any advice would be appreciated.
Thanks in advance,
Keith