donselec
- Aurora, CO, USA
I know that 250.53(E) says basically the part of the bonding jumper which is the sole connection to the supplemental (in this case ground rod) doesn't have to be larger than #6 copper or #4 aluminum. But in this case the inspector says it requires a #4 copper.
On an older house I'm installing a new 200-amp service on the detached garage. It then goes through the garage, underground, and then to the house. There's no water piping at the garage and no rebar to attach to since it's an older building. Therefore the 2 ground rods (we're required in Denver) are the only ground at the garage. He agreed that normally #6 is the maximum size required, but since the rods are the only ground, the conductor has to be sized for the 200-amp service, which is #4. I can't find that in the Code, but he seemed so convinced it just might be true. Any thoughts?