I'm trying to figure out what the actual wording of the requirement means. Sounds like they're saying a #4 or larger copper conductor is inherently protected by the conductor size itself and no further protection is required. A #6 subject to physical damage requires further protection. All of the wording after the bold part below pertains only to #6 and smaller GEC's. Can someone explain this?
250.64(B) Securing and Protection Against Physical Damage.
Where exposed, a grounding electrode conductor or its en-
closure shall be securely fastened to the surface on which it
is carried. Grounding electrode conductors shall be permit-
please note it shall be securely fastened
ted to be installed on or through framing members. A 4
AWG or larger copper or aluminum grounding electrode
conductor shall be protected if exposed to physical damage.
please note it shall be protected from physical damage
A 6 AWG grounding electrode conductor that is free from
exposure to physical damage shall be permitted to be run
along the surface of the building construction without metal
please note is shall be securely fastened
covering or protection if it is securely fastened to the con-
struction; otherwise, it shall be protected in rigid metal
conduit (RMC), intermediate metal conduit (IMC), rigid
if it is not securely fastened then it must be installed in mentioned
polyvinyl chloride conduit (PVC), reinforced thermosetting
methods and be securely fastened per above wording.
resin conduit (RTRC), electrical metallic tubing (EMT), or
cable armor. Grounding electrode conductors smaller than 6
AWG shall be protected in RMC, IMC, PVC, RTRC, EMT,
smaller then 6 AWG is apparently subject to damage no matter
or cable armor.
what other conditions may be
Sure looks like it could be rewritten to me to help it be easier to understand. Funny thing is it looks like the only way to protect a conductor from physical damage is via the mentioned raceways, though I really think the intention is more then just those methods. It only requires protection of an exposed conductor which to me means an enclosed conductor must already be protected so if we place it in a surface mounted enclosure of any type besides what is mentioned - is it exposed or not - and would that be a violation since it is not the mentioned acceptable "enclosures"?
WOW, formatting in the editor and formatting after submitting are not always the same - the blue is my commentary and is broken up some from how I tried to submit it.