1910.147(c)(4)(ii)(D) says...
...and its application to working on electrical conductors is 1910.333(b)(2)(iv) which says...
(B) A qualified person shall use test equipment to test the circuit elements and electrical parts of equipment to which employees will be exposed and shall verify that the circuit elements and equipment parts are deenergized. The test shall also determine if any energized condition exists as a result of inadvertently induced voltage or unrelated voltage backfeed even though specific parts of the circuit have been deenergized and presumed to be safe. [...]"
A couple questions based on the above OSHA requirements:
I have much more to share on this, but I don't want to "lead the witnesses" toward my way of thinking... especially if I'm wrong.
"Specific requirements for testing a machine or equipment to determine and verify the effectiveness of lockout devices, tagout devices, and other energy control measures."
...and its application to working on electrical conductors is 1910.333(b)(2)(iv) which says...
"Verification of deenergized condition. The requirements of this paragraph shall be met before any circuits or equipment can be considered and worked as deenergized.
(A) A qualified person shall operate the equipment operating controls or otherwise verify that the equipment cannot be restarted.
(B) A qualified person shall use test equipment to test the circuit elements and electrical parts of equipment to which employees will be exposed and shall verify that the circuit elements and equipment parts are deenergized. The test shall also determine if any energized condition exists as a result of inadvertently induced voltage or unrelated voltage backfeed even though specific parts of the circuit have been deenergized and presumed to be safe. [...]"
A couple questions based on the above OSHA requirements:
- 147 tells me that for a mechanical LOTO (e.g. clean/inspect of vent fan externals) that merely trying to operate controls is a sufficient verification as long as the fan works and the controls work. But what if the fan is suspected to be jammed? Or what if the control circuitry is suspected of intermittently shorting? Then that check is meaningless.
- 333 tells me that for an electrical LOTO (e.g. 480 fuse replacement inside disconnect) that I must perform two separate checks. First, (A) says I need to operate controls as in 147 above -- but then I have the same questions as above. Second, (B) says I do a live-dead-live type check. I have had workers plea to me that the (B) check counts for the (A) check when the (A) check is 'unfeasible' such as in the examples given.
I have much more to share on this, but I don't want to "lead the witnesses" toward my way of thinking... especially if I'm wrong.