Coworker was ill advised in my opinion and ran a #14 to a 30A dryer for the EGC from panel to outlet. (4 wire - 3#10's and the smaller ground). I too thought this was compliant until I got home and checked.
I was wondering if this is something I now need to correct after the fact?
and would pigtailing the #12 with a #10 from the box and a #10 to the outlet be code compliant?
Trying to avoid returning to fix this. Or at least not having to yank the #14 and repull another EGC.
I was wondering if this is something I now need to correct after the fact?
and would pigtailing the #12 with a #10 from the box and a #10 to the outlet be code compliant?
Trying to avoid returning to fix this. Or at least not having to yank the #14 and repull another EGC.