The reason the NEC wants the correct size EGC if one is provided with a conduit is if a fault ever happen some where inside of the raceway between a ungrounded and the EGC it will still open the OCPD, as Don has said, even the #14 will most likely fault enough current to open the OCPD but conductors smaller then a #10 can build up heat much faster and if the run is long can cause the failure of the insulation before the OCPD opens, so it's not that the pipe can be used as a legal EGC, but that since you have installed a wire EGC it must meet the same requirements as if it was the only EGC because it can fault inside of the conduit to a ungrounded conductor.
Kind of the same idea behind why we must run EGC's sized for the full circuit size in each conduit of a parallel run.