mstrlucky74
- NJ
If you have 3 hots & a neutral is that 4ccc or 3ccc in the raceway? Thanks
Assuming first off it's 3 phase, 4-wire wye system, it could be either. If majority of loads are linear, its 3. If majority is non-linear, then its 4.If you have 3 hots & a neutral is that 4ccc or 3ccc in the raceway? Thanks
1Number of conductors is the total number of conductors in the raceway
or cable, including spare conductors. The count shall be adjusted
in accordance with 310.15(B)(5) and (6). The count shall not include
conductors that are connected to electrical components but that cannot
be simultaneously energized.
In a single phase installation, it would not be legal. :happysad:In a single phase installation it is 4 CCC.
I believe Charlie is talking about shared neutral as I also took the op's question to meanWhat do you mean??
Two hots to an electric dryer and hot & neutral to a washer is not legal.
Neutral Conductors:
Here's some examples of when to count and not count the neutral as a current carrying conductor or CCC:
3?- 208Y/120 or 480Y/277 volt system-different circuit types:
A) 2 wire circuit w/ 1 ungrounded, 1 neutral = 2 CCC's
B) 3 wire circuit w/ 2 ungrounded, 1 neutral = 3 CCC's
C) 4 wire circuit w/ 3 ungrounded, 1 neutral = 3 CCC's*
Notes:
A) A normal 2 wire circuit has equal current flowing in each of the circuit conductors so they both count as CCC's.
B) In this circuit the neutral current will be nearly equal to the current in the ungrounded conductors so the neutral counts as a CCC
C) In this circuit the neutral will only carry the imbalance of the current between the three ungrounded conductors so it is not counted as a CCC, with an exception, *if the current is more than 50% nonlinear (see below for NEC article 100 definition) then the neutral would count as a CCC.
1?- 120/240 volt system-different circuit types:
D) 2 wire circuit w/ 1 ungrounded, 1 neutral = 2 CCC's
E) 3 wire circuit w/ 2 ungrounded, 1 neutral = 2 CCC's
Notes:
D) A normal 2 wire circuit has equal current flowing in each of the circuit conductors so they both count as CCC's.
E) In this circuit the neutral will only carry the imbalance between the two ungrounded conductors so the neutral is not counted as a CCC.
Nonlinear Load. A load where the wave shape of the steady-state current does not follow the wave shape of the applied voltage.
Informational Note: Electronic equipment, electronic/electric-discharge lighting, adjustable-speed drive systems, and similar equipment may be nonlinear loads.