I inherited 1-1/2" EMT conduit 55' long with 25 pcs 12 AWG thhn conductors in commercial kitchen remodel. How can I use those conductors?
I searched forum and it turned out that for motors with fla less than 45% circuit ampacity and pretty much it.
Do you have any other ideas?
from Table 310.15(B)(2)(a) for 21-30 conductors I have to derate them to 45%.
Thank you in advance.