chevyx92
 - VA BCH, VA
Is this allowed by code even though NM isn't allowed above a suspended ceiling in a commercial setting?
Do you mean, for example, in a residential setting, where someone adds a drop ceiling in a basement?
The op stated commercial. It is allowed in residential as you described. Look at 334.12(A)(2)
IMO, it is still not allowed if it is a dropped or suspended ceiling.
I agree the question is ambiguous... but quite simply, NM isn't permitted to be run exposed in dropped or suspended ceilings in other than dwellings.I read the OP as ambiguous on the matter of the type of space. The way the question is worded, to me, asks whether NM is allowed above any fire rated drop ceiling (whatever that is, exactly) even though it isn't allowed, for example, in a commercial setting, without directly saying the fire rated drop ceiling is in a commercial setting.
I could, of course, be reading too much into it, but ambiguity is not your friend when asking code questions.
334.12(A)(2)Please tell us why you think it should not be allowed?
I think not...Residential occupancies are not just 1 & 2 family dwellings- hotels, condos, townhomes ect -- Nm uses are not permited in accessible dropped ceiling are based upon types of construction. Types III, IV, & V ( 3,4,5) are allowed to use NM as long as the install is concealed within walls, floors & ceilings ( a dropp ceiling inaccessible makes the installation concealed) -- You may use NM in commercial buildings as long other sections of the NEC do not prohobit the install (Places of assemblies, Hazardous Locations) to name a few. So wheather the building is residential or commercial has little bearing when it comes to dropped ceilings.
NEC appears to consider it exposed and not permitted in other than dwelling units, including hotels.334.12 Uses Not Permitted.
(A) Types NM, NMC, and NMS. Types NM, NMC, and
NMS cables shall not be permitted as follows:
(2) Exposed in dropped or suspended ceilings in other
than one- and two-family and multifamily dwellings
I think not...
I think not...
If you are referring to Handbook commentary, we both know it's not enforceable and not to be considered an official interpretation. However, that may well be the intent.I disagree NEC 2011 commentary
... If a cable is not considered exposed as per commentary then it must be considered concealed.
With ceiling not defined in Code, we refer to the official dictionary for the definition of "the inside surface at the top of a room".
I leave the final conclusion to anyone reading this...![]()
This statement is not correct in relationship to this discussion as smart pointed out in his comment
You can find this statement in many NFPA documents:I find it interesting that you refer to an official dictionary not part of the code or enforceable to conclude your point. ...
Webster?s Collegiate Dictionary, 11th edition, shall be the source for the ordinarily accepted meaning.