fred trueblood
- elizabeth city n c
2 pole gfi breaker tripping when ground from 10/2 uf is connected ground from either motor using a Gem controller
For a GFCI breaker the neutral for that branch must be connected directly (and only) to the pigtail. That is the only way to force only that branch's neutral current to go through the differential CT inside the breaker.both gfi white tail and grounded conductor connected at same grounding bar
If you wire the neutral pigtail from the breaker properly and you still cannot connect the EGC at the motor without a trip, then either the wiring is wrong (parallel neutral paths) or the motor has gone bad and is leaking current!unit has been installed 3 weeks earlier it was just a nuseance trip ocassionaly, tripping bu now i cannot make a connection to the ground from the motors if the ground is omitted gfi works coarse this is a no no
Tell us one more time about how you connected the neutral pigtail on the breaker? And is it a two pole 240 breaker for a 240V lift motor?have replaced gfi with new not that are you or anyone familiar with Gem
Make sure that the common wire in the low voltage control circuit does not form a parallel path to the power circuit neutral.Gem ties both motors together with acontactor and has a loe voltage tran with a circuit board gives you the ability to funtion remotely
Because a leakage path has developed during the time the lift and motor have been in place and used?pigtail is connected to grounding bar grounding conductor fron 10 2 is connected to middle lug of gfi why did it work some before but not at all now
If there is no neutral wire to the motors, then the circuit neutral is just there to power the control board(s)?are you talking about the grounded conductor it is connected to the motors whitch are grounded to the metal frame of the lift do not have a nuteral
thelow voltage transformer has a nuteral were should it be connected