fred trueblood
Member
- Location
- elizabeth city n c
I have removed all wiring to low voltage and still get same problem
But if your LV control needs a neutral (needs 120V) then you need to use 10/3 (plus ground) NM instead of 10/2. Thanks for catching that Dennis.If you are using 10/2 nm then the ground gets connected to the ground bar not the middle screw of the breaker. That is left empty unless you have a neutral supplied to the equipment-- 10/2 has no neutral if it 240V
do you think a voltage problem because of distance could create a gfi fault?
You mean do you have GFI protection if you use 10/3. Yes you do, by connecting the real neutral wire to the neutral terminal on the two pole GFCI breaker.do you still have gfi protection
no I mean if you connect thegrounded conductor to the grounding bar i will still have gfi protection (Im working for a lawyer dont need any problems)
NO. But only because you do not have a grounded conductor.connecting grounded conductor to ground bar instead of mid terminal of gfibreaker still gives gfi protection and is code compliant?
One more one more thing:thank you very much you have saved me a world of worry and trouble. God bless your soul