gfi tripping for boat lift new construction
If you are using 10/2 nm then the ground gets connected to the ground bar not the middle screw of the breaker. That is left empty unless you have a neutral supplied to the equipment-- 10/2 has no neutral if it 240V
But if your LV control needs a neutral (needs 120V) then you need to use 10/3 (plus ground) NM instead of 10/2. Thanks for catching that Dennis.
no I mean if you connect thegrounded conductor to the grounding bar i will still have gfi protection (Im working for a lawyer dont need any problems)
Whether you connect the grounding conductor to the ground bar (You do NOT have a grounded conductor if you are using 10/2!!!) you will have GFCI protection because the current flowing out on one hot wire must exactly (within 6ma) match the current in the other hot wire. That is exactly the protection you need. Since you have no neutral, you will connect nothing to the neutral terminal on the breaker but you must connect the EGC (bare copper in the 10/2) to the ground bar in the panel.
connecting grounded conductor to ground bar instead of mid terminal of gfibreaker still gives gfi protection and is code compliant?
NO. But only because you do not have a grounded conductor.
Rephrasing your words properly:
"connecting grounding conductor to ground bar instead of mid terminal of gfibreaker still gives gfi protection and is code compliant?"
The answer to that would be YES.
thank you very much you have saved me a world of worry and trouble. God bless your soul
One more one more thing:
For at least some two pole GFCI breakers you do have to connect the white neutral pigtail from the breaker to the neutral bar in the panel even if you do not connect anything to the neutral screw on the breaker.