Razzap
Member
Take a look at the attached photo. This is an exterior subpanel feeding multiple Recreational Vehicle sites. Three of the direct burial aluminum neutrals have been removed from the neutral bar and terminated under ONE copper #6 AWG (?) using a hose clamp. The copper wire appears to have an automotive type of insulation, not NEC type. The panel is Cutler-Hammer with Square D, Seimens, and other brands of CB's installed. There is no cover over the breakers, the panel interior is accessible just by opening the (unlocked) door. I see little or no anti-oxidant on any of the wires. I am sure there are other violations as well, including the only support of the panel is the PVC stubbed underground, subject to mower and snow plow damage. I am currently working up a design and quote to upgrade the entire park.