As promised, here's the next chapter in the story of our beleaguered wire pulls...
As first described in this post last year, and then discussed again in this post this year (see "Problem 1"), our #4 250kW solar inverter had tripped its 400A breaker in our PV distribution panel several times in the past. I had long suspected that the 500MCM CU-XHHW-2 inverter branch circuit conductors (which, btw, I had incorrectly referred to as "inverter feeders" in past posts) were damaged, but the problem was intermittent and the installation contractor was never able to trace the fault, largely due to the fact that he was too cheap to own a megger.
When we had our facility's main feeders (installed by the same contractor) blow-up earlier this year, we had all the solar AC wires meggered by an independent testing company. They confirmed that one of the wires to our #4 inverter had leakage. This was the set of conductors that the contractor pulled the wrong way through an LB as illustrated in this photo:
I had watched them pull these wires in during the original installation and knew at the time that the insulation had to have been damaged as they used a tractor to pull -- with great strain -- the final loop of those large wires in through that LB. So I was not surprised by the results of the testing agency and I told the property owner and the installation contractor where I thought the wire damage was located, namely between the LB and the inverter. My recommendation was that the inverter be removed from the pad and the conduit be disassembled back to the LB. The damaged wire could have been cut out and the LB could have been replaced with a weatherproof wireway to contain the splices for the repairs.
So imagine my surprise when the contractor reported repairing the wire after having the inverter offline for only 45 minutes! This was his "repair" on our 480V/400A wires:
LB Left Entry:
LB Back Entry:
That's right: he opened the LB and brushed some Liquid Tape on the wires and then used some peeled-off LFMC outer jacket material to sleeve his repairs! I suspect the LFMC jacket is providing more dielectric strength than the thin layer of dried Liquid Tape.
I can't believe this is an acceptable repair. But I need some solid NEC or UL references to back up my argument. Advice please!
As first described in this post last year, and then discussed again in this post this year (see "Problem 1"), our #4 250kW solar inverter had tripped its 400A breaker in our PV distribution panel several times in the past. I had long suspected that the 500MCM CU-XHHW-2 inverter branch circuit conductors (which, btw, I had incorrectly referred to as "inverter feeders" in past posts) were damaged, but the problem was intermittent and the installation contractor was never able to trace the fault, largely due to the fact that he was too cheap to own a megger.
When we had our facility's main feeders (installed by the same contractor) blow-up earlier this year, we had all the solar AC wires meggered by an independent testing company. They confirmed that one of the wires to our #4 inverter had leakage. This was the set of conductors that the contractor pulled the wrong way through an LB as illustrated in this photo:

I had watched them pull these wires in during the original installation and knew at the time that the insulation had to have been damaged as they used a tractor to pull -- with great strain -- the final loop of those large wires in through that LB. So I was not surprised by the results of the testing agency and I told the property owner and the installation contractor where I thought the wire damage was located, namely between the LB and the inverter. My recommendation was that the inverter be removed from the pad and the conduit be disassembled back to the LB. The damaged wire could have been cut out and the LB could have been replaced with a weatherproof wireway to contain the splices for the repairs.
So imagine my surprise when the contractor reported repairing the wire after having the inverter offline for only 45 minutes! This was his "repair" on our 480V/400A wires:
LB Left Entry:

LB Back Entry:

That's right: he opened the LB and brushed some Liquid Tape on the wires and then used some peeled-off LFMC outer jacket material to sleeve his repairs! I suspect the LFMC jacket is providing more dielectric strength than the thin layer of dried Liquid Tape.
I can't believe this is an acceptable repair. But I need some solid NEC or UL references to back up my argument. Advice please!