Here's the latest update on this fiasco. Our general manager informed the contractor that the liquid tape repair to these damaged conductors was insufficient and that a proper repair needed to be made, namely cutting out the damaged sections of wire and splicing in new wire. The following was his response:
So his position is that because the wires passed a megger test, then his repair is good. Of course, I could have wedged a styrofoam packing peanut between the damaged insulation and the metal edge of the LB outlet and that too would have passed a megger test.
We've told him that we're not accepting this work and, if he still refuses to make a satisfactory repair, that we will hire another contractor to do the work and bill him for the costs. So at this point, it looks like we may be headed for litigation. Are there any other code references or regulations that we can use to support our stand on this issue?
"Regarding the inverter AC wires, we [repaired the wires to] inverter #4 that were recommended to be replaced in the April 21, 2014 report by [the third-party testing company]. As stated in [testing company] report, 6/13/14, these wires tested satisfactory as found and are operational and acceptable for service. No further work will be conducted on these wires."
So his position is that because the wires passed a megger test, then his repair is good. Of course, I could have wedged a styrofoam packing peanut between the damaged insulation and the metal edge of the LB outlet and that too would have passed a megger test.
We've told him that we're not accepting this work and, if he still refuses to make a satisfactory repair, that we will hire another contractor to do the work and bill him for the costs. So at this point, it looks like we may be headed for litigation. Are there any other code references or regulations that we can use to support our stand on this issue?