Some interesting email traffic with local electrical inspector.
Thoughts?
I recently requested an electrical rough inspection on one of my residential jobs. This job contained approximately eight (8) locations of where a wall light, ceiling light or outlet would be required, yet the specific location was to be determined at a later date. Of these eight locations four are bathroom vanity light walls. In these instances it is common work practices to loop an NM cable in the walls or ceiling with enough cable to allow for more than one option in actual fixture or outlet final placement.
This is common in these large custom homes due to many factors beyond my control as the licensed electrical contractor. In these instances, we come back to job after the finished surface has been installed and cut holes for specified light or outlet boxes. These boxes are installed and used in accordance with NEC and the instructions included in the listing and labeling.
I received a Violation Correction Notice that had one violation listed that I would like to review with you concerning the above described conditions.
1.Cannot use cut in boxes (old work) on open walls.
I met with the inspector on site to review the two violations in person. I asked the inspector how could a rough in inspection fail for using old work boxes on open walls, when there are not any old work boxes currently installed. He stated that I would not be allowed to use an old work box anywhere in this project, as it is a new construction project. He then stated that old work boxes are to be used in remodel projects only.
I then asked for an NEC reference. I was given 110.3(B) and 314.23.
110.3(B)- Installation and use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling. (NEC 2011)
I have studied the instructions and spec sheets for the old work boxes. I do not see any indication or direction in the instructions in regards to new construction or remodel use specifically.
I also have done some research in regards to the UL listing. I have located a letter from a UL engineer on the subject. Please take a moment to review.
(http://www.mikeholt.com/technical.p... fixtures used in new construction? (8-10-2K)
I also contacted the manufacturer for some clarification. I have attached the instructions and the email from the manufacturer. The manufacturer stated ? it is quite common for old work boxes to be used in new construction (many applications where there may not be a stud to attach to,etc.)?
314.23- Enclosures within the scope of this article shall be supported in accordance with one or more of the provisions in 314.23(A) through (H)(NEC 2011)
314.23(C)- Mounting in finished surfaces. An enclosure mounted in a finished surface shall be rigidly secured thereto by clamps, anchors, or fittings identified for the application.(NEC 2011)
I asked the inspector to clarify how I would not meet this requirement by installing the box during the trim out stage of the project. I would be mounting the box in a ?finished surface?. I also pointed out to the inspector a wall on this projected was open on one side and still had drywall on the other side. I had installed an old work box for an added light switch in the closet on the ?finished surface? side. He stated that was non-compliant installation of the box. I asked him to clarify to me how he felt that the existing finished surface side did not meet 314.23(C). He stated that it was only 50% finished and the open wall on the other side meant that I would be required to use a structure mounted plastic box.
It was explained to me that the position and interpretation of this requirement was that the term ?finished surface? is to be defined as after the city has issued a CO and all work was completed on the project. He stated that if I used an old work box during the trim he would have us remove drywall and mount the light, outlet boxes to the structure and make repairs to finished surfaces.
This interpretation basically removes the use of an old work box from my arsenal of tools to earn a living as well as satisfy my customer?s needs.
I would respectfully request that you review the interpretation and enforcement of this issue.
Sincerely,
Inspector?s response:
Sir,
I am sorry that you disagree with our decision however the code is clear on the support requirements for boxes installed in new construction and by definition this is an ?old work? box one can only assume it pertains to existing conditions. Therefore if the walls are open and the new boxes can be supported then they should be according to article 314.
Thank You
Thoughts?
I recently requested an electrical rough inspection on one of my residential jobs. This job contained approximately eight (8) locations of where a wall light, ceiling light or outlet would be required, yet the specific location was to be determined at a later date. Of these eight locations four are bathroom vanity light walls. In these instances it is common work practices to loop an NM cable in the walls or ceiling with enough cable to allow for more than one option in actual fixture or outlet final placement.
This is common in these large custom homes due to many factors beyond my control as the licensed electrical contractor. In these instances, we come back to job after the finished surface has been installed and cut holes for specified light or outlet boxes. These boxes are installed and used in accordance with NEC and the instructions included in the listing and labeling.
I received a Violation Correction Notice that had one violation listed that I would like to review with you concerning the above described conditions.
1.Cannot use cut in boxes (old work) on open walls.
I met with the inspector on site to review the two violations in person. I asked the inspector how could a rough in inspection fail for using old work boxes on open walls, when there are not any old work boxes currently installed. He stated that I would not be allowed to use an old work box anywhere in this project, as it is a new construction project. He then stated that old work boxes are to be used in remodel projects only.
I then asked for an NEC reference. I was given 110.3(B) and 314.23.
110.3(B)- Installation and use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling. (NEC 2011)
I have studied the instructions and spec sheets for the old work boxes. I do not see any indication or direction in the instructions in regards to new construction or remodel use specifically.
I also have done some research in regards to the UL listing. I have located a letter from a UL engineer on the subject. Please take a moment to review.
(http://www.mikeholt.com/technical.p... fixtures used in new construction? (8-10-2K)
I also contacted the manufacturer for some clarification. I have attached the instructions and the email from the manufacturer. The manufacturer stated ? it is quite common for old work boxes to be used in new construction (many applications where there may not be a stud to attach to,etc.)?
314.23- Enclosures within the scope of this article shall be supported in accordance with one or more of the provisions in 314.23(A) through (H)(NEC 2011)
314.23(C)- Mounting in finished surfaces. An enclosure mounted in a finished surface shall be rigidly secured thereto by clamps, anchors, or fittings identified for the application.(NEC 2011)
I asked the inspector to clarify how I would not meet this requirement by installing the box during the trim out stage of the project. I would be mounting the box in a ?finished surface?. I also pointed out to the inspector a wall on this projected was open on one side and still had drywall on the other side. I had installed an old work box for an added light switch in the closet on the ?finished surface? side. He stated that was non-compliant installation of the box. I asked him to clarify to me how he felt that the existing finished surface side did not meet 314.23(C). He stated that it was only 50% finished and the open wall on the other side meant that I would be required to use a structure mounted plastic box.
It was explained to me that the position and interpretation of this requirement was that the term ?finished surface? is to be defined as after the city has issued a CO and all work was completed on the project. He stated that if I used an old work box during the trim he would have us remove drywall and mount the light, outlet boxes to the structure and make repairs to finished surfaces.
This interpretation basically removes the use of an old work box from my arsenal of tools to earn a living as well as satisfy my customer?s needs.
I would respectfully request that you review the interpretation and enforcement of this issue.
Sincerely,
Inspector?s response:
Sir,
I am sorry that you disagree with our decision however the code is clear on the support requirements for boxes installed in new construction and by definition this is an ?old work? box one can only assume it pertains to existing conditions. Therefore if the walls are open and the new boxes can be supported then they should be according to article 314.
Thank You