ceb58
- Raeford, NC
Where does the OP state that the doors were installed after the building inspection.
"The building inspector approved the work 2 years ago, but sent us a letter that the electrical inspector told him that it is not correct due the NEC 2011 230.2 and 230.72."
If the demising wall was new then, how does 230 come into play as a violation when it was first built? What some are saying that building a demising wall this would allow a second service.
Something else is going on here and it appears it is a 2 year old issue.
We installed a man door and a garage door into that demising wall.
Looks as this is what happened. The existing fire wall, by building code, made the structure 2 separate buildings. Thus allowing the 2 separate services.
Building inspector approved the doors to be cut in.
Some one did not know or missed the codes about fire rated doors in a fire rated wall.
Electrical inspector has now caught the violation.
Install the fire doors and you are back to 2 separate structures.
I did a large addition to a fire department last year. The new addition was joined to the old with a 2 hr rated wall. It went across 90 ft to another 2 hr rated wall that now separated the new truck bay from what will be sleeping quarters. For practicality I installed a second service on the new part of the building that was separated by the second fire wall. But before any of this was done I ran every thing by the inspector (combo). His ruling was what I wanted to do was fine. He went further to say that by building code I could have 3 separate services because of the 2 fire walls. The existing service, a service for the truck bay and a service for the sleeping quarters. The only thing he stressed was that I follow 230.2 (E). He said in case the fire department caught fire he wanted the fire department to know where the services were. :happyyes: