lielec11
- Charlotte, NC
- Electrical Engineer (PE)
Where in NFPA 70E does it list the incident energy levels and the associated PPE categories (i.e. 0 < 1.2cal/cm2)? I cannot seem to find it.
NFPA 70E-2012 Table 130.7(C)(16) Protective Clothing and Personal Protective Equipment (PPE)
I saw this one, however, where does it relate to incident energy levels?....Where is this defined?
It is not.
70E determine a Hazard Risk Classification (HRC) based on the task being performed, it then goes on and provides a table that says what incident energy level PPE must have based on the HRC.
While it has been a common industry practice to 'go backwards' and relate PPE levels to incident energy, this practice has been frowned upon by 70E committees.
It is not that much different from what a fire fighter wears at a fire and they don't have issues with it. In the training for my HazMat Tech B certificate, they had us in full suits, including 5 layers of gloves and you had to work with hand tools and bolts and nuts. In one part they tossed coins on the ground and you had to pick them up. Sure it is more difficult to work, all suited up, but if something happens, you will sure wish you had the proper PPE on.On another note, how can one work safely wearing an arc rated hood, suit and jacket? They are so bulky I can't imagine being able to perform some of the tasks that require all this gear.
As a side note, there are very few tasks you are permitted to perform while the equipment is energized. Just because you have the PPE does not mean that you are permitted to work on energized equipment.