Question on UFER ground with 2 panels
KWH
I will have 2 main breaker panels ( from c.t. cabinet ) can you install 1 ufer ground to 1 panel and split bolt off this ground to the other panel beside it.
Is there still a requirement to use only a non-reversible connection when it comes to gec's.
If so the split bolt may not be compliant but a crimp connection would be?
In the installation you describe a split bolt (listed as suitable for grounding and bonding) would be compliant. See 250.64(D)(1).
You could also use a common ground bar as allowed by 250.64(D)(1)(3). If you use this option the bar must be a busbar 1/4" X 2" X whatever required length to attach all GECs and jumpers. You can also use non crimp type connectors in this scenario as well.
Couldn't resist throwing the busbar idea out there.:D
Yes because the conductor from the CEE to the first panel is the GEC. The conductor from the split-bolt to the second panel is a bonding jumper. Only the GEC is required to be continuous or irreversibly spliced.
You MUST have stock in a buss bar company :D