- Tennessee NEC:2017
- Semi-Retired Electrician
I looked at a job that the customer wants a way to plug in a number of pieces of equipment to test them to see if they are operational. They want to be able to have single phase and 3ph power available on their testing station.
What they would like is some type of box or panel large enough to accommodate several receptacle configurations, both single and 3 phase. They also want this to be portable or a way to disconnect it and move it when not in use.
Basically they want a cord & plug that would supply 3ph power to the box and distribute the power to each receptacle according to the receptacle requirements, some single ph and some 3ph.
They will only be using one receptacle at a time. The reason they want this is they buy used equipment and need to verify that it works before reselling it.
Is there a compliant way to do this?
How would you know how to fuse this not knowing the loads that will be plugged in?
The feed to this would have to come from the overhead bus. So I would need to use the correct size fuses in the bus disconnect. Would the portable box/panel also need OCPD?
Any ideas/comments would be appreciated.