PVC COATED MC TYPE CABLE REQUIREMENTS
TOXICSTUFF
ST CHARLES, MO
I have searched all over the code for this product. and I cant seem to find any articles relating to this type of cable. Basically in this building the GC is going to pour a 3" concrete topping on top of existing concrete. My question is can this PVC Coated MC cable be buried in this 3"topping? if so, where is it at in the code book?
Thank you
Based on Southwire's website it would appear it would be o.k. but I would definitely clear such use with the AHJ & Building (structural) inspector.
[h=2]Applications
[/h] Southwire Armorlite ? Type MC Cable - "flame retardant sunlight resistant PVC Jacket" is suitable for use as follows:
  • Direct burial applications, installation in concrete and where exposed to cinder fills, strong chlorides, caustic alkalis, or vapors of chlorine or of hydrochloric acids.
  • Branch, feeder and service power distribution in commercial, industrial, institutional, and multi-residential buildings.
  • Power, lighting, control, and signal circuits.
  • Fished or embedded in plaster.
  • Concealed or exposed installations
  • Places of Assembly per NEC 518.4 and theaters per NEC 520.5.
  • As aerial cable on a messenger.
  • Installation in cable tray and approved raceways.
  • Under raised floors for information technology equipment conductors and cables per NEC 645.5(D) & 645.5(D)(2).
  • Class I Div. 2, Class II Div 2, & Class III Div. 1 Hazardous Locations.
The applicable code sections are 330.10(11) and 330.12(2)
Thank you for your findings. I am aware that this cable is allowed to be used in concrete. My question is how deep must it be concealed in the concrete? would this be in working clearances? Were looking for an arcticle so we can present this to the AHJ.
There is no minimum cover distance when embedded in concrete in the NEC.
Although where concrete cover is required rather than optional there are depth numbers.
There may be structural or other reasons not to have the void too close to the concrete surface, but that is not an NEC concern.
any type MC-HL will work you might want to look at TC-ER as well but I dont know off the top of my head if it will meet code
Type TC (includes TC-ER) is not permitted to be "Installed outside a raceway or cable tray system, except as permitted in 336.10(4) and 336.10(7)".
336.10(4) is messenger-supported outdoors.
336.10(7) applies to industrial establishments (see section for details).