sub panels

Status
Not open for further replies.

merc66

New member
Location
edison,nj,usa
200 amp 120/240v main breaker from distribution board to feed 2 120/240v panels in a double wide trailer that is being used for pop warner football team.IT has to be run underground.what size wire can urd cable be used and do i have to install a groundrod?
 
200 amp 120/240v main breaker from distribution board to feed 2 120/240v panels in a double wide trailer that is being used for pop warner football team.IT has to be run underground.what size wire can urd cable be used and do i have to install a groundrod?

is URD even a NEC wiring method?

in any case, you will need 2 hots, a N, and a ground. I seem to recall URD only has 3 wires.

do you think the trailer qualifies as a structure? if so, it needs a grounding electrode system.
 
URD is often a generic term for USE. If it is truly URD then it would not be legit and could not be installed in the trailer. Most USE is dual rated and compliant
 