140815-0913 EDT
GITRDUN:
I believe your troubleshooting idea was to power down the CNC, open the disconnect, check the state of the breakers, put all breakers in the off state, close the cabinet door, and in the morning see if anything failed.
I do not believe most, if any, of the breakers isolate the circuit areas where your failures have occurred. In my post numbered 36 the listed small breakers are for coolant pump, another motor, user outlet, solenoids, etc.
None of these have anything to do with the AC side of the servo motors or main spindle. One breaker relates to the solenoids. The servo motors and main spindle appear to be limited only by the main disconnect/breaker.
Since you have indicated that one or more of the small breakers have tripped, possibly in association with other failures, then it is important to know which breakers tripped.
A useful experiment would be to have the cabinet door open at the time the machine was powered down. I don't know how to open the door with the disconnect on. Were the disconnect a Sq-D, then it is easy. If there is no way to override the mechanical interloack, then the only way is to open the door close the disconnect, mostly close the door, and run with the door just open a crack. It would be important to know if any of the breakers trip at the time CRM drops out. Any failure before power down would cause the machine to not function, and this has not been mentioned.
By any chance were line reactors added to the 3 phase input lines to the machines?
.