- Location
- Illinois
- Occupation
- retired electrician
If I have an industrial installation with no line to neutral loads and a 3 pole transfer switch can I install a system bonding jumper in the transformer and a second one in the generator and run supply side bonding jumpers from both the transformer and the generator to the transfer switch? The feeder conduits between the transfer switch and both sources of supply will have three 500 kcmil and a 1/0 system bonding jumper in each conduit.