iceworm
Curmudgeon still using printed IEEE Color Books
- Location
- North of the 65 parallel
- Occupation
- EE (Field - as little design as possible)
This is all on the plant side of the service. The system is 480y/277 solidly grounded, but with no line to neutral loads. The transformer is 2000 kVA and the gen set 2000kW. Eight sets of three 500's with 1/0 supply side bonding jumpers between the two sources and the ATS.
The transfer switch is rated at 3,000 amps. It is a GE/Zenith switch, but not sure of its construction. ...
Okay. Did not know that from the first post. I still don't have any experience with large transfer switches - all I have seen are in switchboards. And I did not do the designs. Still the physics is the same.
So, I'm guessing: the conductors are installed, the gen NG bond is installed, the xfm NG bond is installed. And, it is no longer an option to pull in a neutral separate from what you are calling the supply side bonding jumper.
And the issue is to figure out if the installation meets code - as in this is an AHJ problem? Or are you trying to figure if the install is a good design - as in a customer spec issue? These are really two separate issues.
That's true, 250.24.C applies to services. However, the system still has an NG bond in two locations. Not a good idea. However, as you said, in this case, it shouldn't matter - hopefully true.I am not aware of a requirement to run the grounded conductor to the first disconnect for an SDS. It is there for a service, but not there for an SDS.
I won't be any further help in a code discussion. Previous posts have that well covered
However:
Looking at this from a design standpoint. You have two paralleled non-SDS feeders separated by 3pole CBs - probably with paralleling gear. And the neutrals are solidly connected through 8 - 1/0 CU.
If this is the case, a code discussion, while interesting, doesn't change these were not particularly good design choices. This is not a cookie cutter installation suitable for a code designed project.
Two that come to mind are:
- GF protection. Where is that exactly? Even though there are no line-neutral loads, I can see that as being a problem.
- And, of course, isolation for maintenance.
After it is decided the installation meets code, I'd be interested in how these two are handled.
ice