- Placerville, CA, USA
- Retired PV System Designer
Very much too small if no current at all flows on the utility neutral, as in the original problem.Current flowing on utility ground because Service Neutral is too small.
As Wayne (hurk27) said, I believe you are confusing GES with EGS... but not just that. I think you are further confusing contingent with intended. The whole grounding system is intended to mitigate hazards should they occur. It is not intended to mitigate avoidable hazards, and inadvertently reduce the likelihood of detection and remedial action.The NEC is clear that the purpose of the GES (Grounding Electrode System) is to provide an effective low impedance path to operate the overcurrent protection when a fault occurs.
****That is to say, Fault Current is intended to flow in the GES. Period. It's just that simple.*****
The NEC is SILENT about isolating the path of the current in the conductors that comprise the GES. Think about that. A lowly #14 Equipment Grounding Conductor (EGC) out on the end of a branch circuit IS NOT PREVENTED from being connected to EARTH. The instant that happens, the EGC is another parallel path back to the source.
The NEC is also SILENT about deliberately introducing connections of the EGC to Earth. . . both of these silences mean that if there is a circuit completed from the Main Bonding Jumper to Earth and back to the Source as a parallel path along an EGC, or even a GEC, that it just IS.
If that isn't INTENDING to allow current in parallel paths, I don't know what is.
It does not tell us anything about the load current. It just says that there is current in the GEC and zero current in the neutral on the utility side of the ground/neutral bond.I don't see in the example where it says there is no current being drawn by the load.
But I would believe it is unavoidable in many cases and very acceptable by the NEC, all GEC's are in fact parallel with the utility neutral, they will always share the neutral current proportionally to the impedance of the path, many water pipe GE's are simply a parallel path through the neighbors house GE then back of their neutral to the transformer, these water pipes can be allot lower impedance then the MGN and or the involved service neutrals so having a current on the GEC can be quite normal, sometimes we might see a little of the primary current on this path because the water lines can also parallel the MGN between the houses down the street via the same GEC connections at each house, but I would expect that this current would be very small, a lost MGN connection could raise it a bit but over all it would be small because of the amount of current involved so unless this current is very large or there is a high voltage potential (10 volts or more ) to remote earth from the grounding this is allot of worrying over nothing.
For mike to suggest cutting the water pipe at the 10' mark from the house and put in an isolator to me would make the system much more dangerous because even though it is not an intended current path, it does provide some safety backup for a lost neutral condition, lightly dimming and brightening of lights is a lot better than having all the electronics burning up and or a fire breaking out because of a over voltage condition, a home owner should always be instructed to have an expert check out the service neutral anytime they see lights getting dimmer and brighter, even if it is not by much.
Mike just because you may have current on the GEC it does not mean you have a large difference of voltage potential between equipment or earth, if you think you have a problem then always measure the voltage between the service or grounding system and remote earth, if it is higher then 10 volts then you have a problem, but I have seen many times for it to be around 3 to 5 volts and be very normal because it is nothing but the normal voltage drop of the service neutral, only when we have a body of water where we have people normally in it such as pools and lakes/rivers with boat docks then even 3 volts can be a problem, but when we start seeing over 10 volts we know there is a problem with the neutral or transformer primary neutral or MGN, then we must act.
I still don't see where everyone is assuming there is zero current on the load side of the neutral.
I know Don said there was not . Don was that just because he did not mark the drawing with the
load amperage or what?
Or did the OP say there was no load on the neutral and I missed it some where?
The way I look at this is the main is in the up position and unless every thing on the load side of the neutral
is cut off in some way there should be a load on the neutral.
With a very long service drop and with a city wide metal water line as the grounding system this would be common place to have a large voltage drop that the ground would pick up the difference in the drop if there was a fault.
Its not a fault unless something on the load side of the main has a neutral to equipment ground touching some where down stream of the main.
I 'm sorry if I just repeated what some one else has already said, if so I agree.
There might not be any thing wrong here at all other than just the allowable voltage drop.
Just because there is a voltage between the neutral and ground doesn't mean there is a fault
with the service.
Ron(?)
My example was meant to be vague. If the 'return current' is not going back on the utility neutral and is going back via the public metal water lines (to the source) how would you answer the poll? Forget voltages. Don't put too much thought into it.
If its not going back on the utility neutral and on the ground that leaves nothing but a open neutral.
Please direct me to the post where you stated that and not some one else's assumetion,
"If the 'return current' is not going back on the utility neutral and is going back via the public metal water lines"
Thanks for the reply
You gave away the answer too soon, I thought that was obvious with some assumption from the information provided.
Or if structure one is the only one on the transformer, it could still be leaving structure one and returning to the transformer secondary via the utility secondary ground.This is a thought question. Not a 2+2 (code) question.
Please look at the limited graphic that I started with.
It (neutral current) is leaving structure #1 and entering structure #2 via the water lines. Then back to the source.
I agree... but as witnessed here, there are those that believe neutral current through the GES and supply-side bonding is intended. It is a consequence of grounded systems and bonding, but it is not intended under nominal conditions. Taking measures to reduce neutral current under nominal conditions could actually impose a greater hazard under abnormal conditions. The underlying principle of system grounding is to minimize hazards under abnormal conditions. If anyone considers taking measures under 250.6, they should analyze how it would affect the system under abnormal conditions before proceeding.... My point being, alternate paths for neutral current are absolutely unavoidable...
I can't find an emoticon for applause. If I could I would use it here......Our bed was made for us long before we were born; we live on an MGN continent, and therefore we must continue on in the same way because the lot has been cast.
People seem to spend more time chasing their tails worrying about bad grounding boogeymen and the like, and they end up failing to observe basic workmanship in their terminations, which ironically winds up ferrying current onto their grounding conductors!
:slaphead:
Smart, you make a lot of sense sometimes and are very sharp but in this case IMO you are splitting hairs over nothing.
Intended or not it is a result of NEC requirements and in reality causes little if any problems in premises wiring systems.
Personally I think 250.6 should be removed unless they define objectionable current and spell out the allowable remedies if it exists.
Geeesh, Bob. I essentially said the same thing you did... just a bit more wordy. :roll:Smart, you make a lot of sense sometimes and are very sharp but in this case IMO you are splitting hairs over nothing.
I believe it is required. 250.6(B) general statement, in effect, states alterations cannot defeat the requirements of 250.4(A)(5) and (B)(4).No I do not believe that thinking about abnormal conditions is required in the code.
That picture is a demonstration of neutral current on an EGC... not a GEC. It is a non-compliant installation, so it has no bearing on the issue being discussed.In my example it is considered objectionable because the GEC and copper metal water lines are 'acting' as a neutral. Violation.
It is no different than this:
In the original OP condition, some of the current on the GEC was fault current... which is not objectionable current by my understanding (correct). The only problem I see is fault detection.
After the utility neutral fault was corrected, the remaining current through the GEC cannot be attributed definitively to objectionable current as long as Code lacks a definition for such.
First, with no Code definition for objectionable current, how can you really classify it as such? It comes down to a matter of opinion... and I'll give you that.My alteration ("Alterations to Stop Objectionable Current.") does not - why I put those two sections in my post.
Follow up question. Now that the utility made a repair there is still objectionable current on the copper metal water lines I say that this should be removed by isolating the water lines (10'+; 250.52(A)(1)) outside. One of my concerns is that since the GEC is bare copper and runs in a chase with the interior copper water lines and metal HVAC runs that it 'may' be coming in contact with these interior parts. I say replace it with an insulated GEC (connected within 5'; 250.68(C)(1)) to remove any touch potential on these parts.
It's only 'like' in the sense there's neutral current on a grounding conductor. But using a non-compliant scenario to make a point is not a good way to go about it IMO.The picture shows a 'like" condition. It does have bearing or I would not have used it.
Correct me if I'm wrong, but the OP was a fault condition: open service neutral. You later said that was corrected. What we're talking about now is a normal, compliant condition.I'm the OP and the current was NOT fault current it was neutral current returning to the source. No "fault" was corrected.
I agree with that in regards to neutral current on the equipment grounding system... but it is not explicit enough to prohibit neutral current on the grounding electrode system. Even if there is no low-impedance pathway you will still have some current transferred through earth.IMHO neutral current is only permitted on the grounded conductor in a 'normal' condition.