Geeesh, Bob. I essentially said the same thing you did... just a bit more wordy. :roll:
Sorry, it did not come across to me that way.
Could be my mistake.
Geeesh, Bob. I essentially said the same thing you did... just a bit more wordy. :roll:
I believe it is required. 250.6(B) general statement, in effect, states alterations cannot defeat the requirements of 250.4(A)(5) and (B)(4).
My alteration ("Alterations to Stop Objectionable Current.") does not - why I put those two sections in my post.
jxofaltrds said:In my example it is considered objectionable because the GEC and copper metal water lines are 'acting' as a neutral. Violation.
jxofaltrds said:IMHO neutral current is only permitted on the grounded conductor in a 'normal' condition.
Neutral Conductor. The conductor connected to the neutral point of a system that is intended to carry current under normal conditions.
I'm really lost. I don't see a diagram or a question, just a choice of answers to a invisible question......
My alteration ("Alterations to Stop Objectionable Current.") does not - why I put those two sections in my post.
The picture shows a 'like" condition. It does have bearing or I would not have used it.
I'm the OP and the current was NOT fault current it was neutral current returning to the source. No "fault" was corrected.
IMHO neutral current is only permitted on the grounded conductor in a 'normal' condition.
Neutral Conductor. The conductor connected to the neutral
point of a system that is intended to carry current under
normal conditions.
....
So you need to stop worrying about parallel neutral currents ahead of the main service disconnects because the NEC has requirements that is going to cause them, and there's no way around them in a code compliant installation.
Rem....
First these are not ahead of the main disconnect. They are made at the disconnect.
I do worry about current taking paths back to the source that can harm individuals.
I still hold my Plumbing License even thought I no longer do contracting. With my plumbing hat on now - I use to carry car jumper cables when I had to repair (cut) copper water lines. One because I didn't like the sparks and two when I understood that neutral current could be on the lines because of a lost POCO neutral. I didn't want to get hurt. What about the water co employees?
What if Joe Homeowner repairs his own pipes and doesn't have our knowledge? What if he uses a quick repair coupler and isolates a connection to the water line (not with in 5' like the old days) and he has no POCO neutral?
My point is once we know that there is a potential problem I believe that we must correct it.
Help me here. Wasn't the water line one of the first electrodes? Is it time to revisit its use?
Just because we use to do it doesn't make it right. We use to test with our fingers. We use to stick fingers up the rectum for electrocution victims.
Many electronic controls and computer equipment are sensitive
to stray currents. Circulating currents on EGCs, metal raceways,
and building steel develop potential differences between ground
and the neutral of electronic equipment. Installation designers
must look for ways to isolate electronic equipment from the
effects of such stray circulating currents.
Isolating the electronic equipment from all other power equipment
by disconnecting it from the power equipment ground is not
the right solution, nor is removing the equipment grounding means
or adding nonmetallic spacers in the metallic raceway system. These
solutions are contrary to fundamental safety grounding principles
covered in the requirements of Article 250. Furthermore, if the electronic
equipment is grounded to an earth ground that is isolated
from the common power system ground, a potential difference is
created, which is a shock hazard. The error is compounded because
such isolation does not establish a low-impedance ground-fault
return path to the power source, which is necessary to actuate the
overcurrent protection device. Section 250.6(B) is not intended to
allow disconnection of all power grounding connections to the electronic
equipment. See the commentary following 250.6(D).
Geeesh, Bob. I essentially said the same thing you did... just a bit more wordy. :roll:
I don't think it is your mistake, Bob.Sorry, it did not come across to me that way.
Could be my mistake.
Actually it is...I don't think it is your mistake, Bob.
The turn in this thread has me realizing, recalling some of my other similar exchanges with you, Smart, that I would benefit from unpacking your meaning of "intended".
This is not a uncommon thing on services with a high voltage drop on their feeder.
I understand your concern for safety. Like you said it could be a loose or open neutral.
I am assuming you had a amp clamp around the main bonding jumper?
If it had been me I would have turned the main power off and took the bonding jumper off
then turn the power back on and took a voltage reading from my neutral to the ground if it is less than a few volts which it usually is.Then you can make the assumption that it is just the NEC acceptable voltage drop
from a long feeder or the reduced neutral size for the single phase 120/240.If you don't trust your
meter take a 12 volt bulb and test it.
I have removed grounds on some services during trouble shooting and have seen sparks like a arcing welder.
Measure the voltage and sometimes would be less than a few volts. But the amperage would be very high.
It was no more than voltage drop and the utility ground trying to conduct that voltage drop.
Ronald
Actually it is...
You both remember previous discussion regarding objectionable current and "reading between the lines" of my post. If you recount earlier discussions in their entirety, you'd realize those were regarding neutral current on service conduits between enclosures. I've never combined that and neutral current on the GES into one concept... and the discussion here is regarding neutral current on the GES.
To call the part of the total unbalance current that is traveling in any one of the multiple parallel paths as "neutral current" is, in my opinion, not possible.If you recount earlier discussions in their entirety, you'd realize those were regarding neutral current on service conduits between enclosures. I've never combined that and neutral current on the GES into one concept... and the discussion here is regarding neutral current on the GES.
You can look at it that way... but IMO, and quite likely many others (but I'll let them speak for themselves), you are wrong.To call the part of the total unbalance current that is traveling in any one of the multiple parallel paths as "neutral current" is, in my opinion, not possible.
In my mind, "neutral current" exists only inside the insulated path on the load side of the Main Bonding Jumper in either the modern not-re-grounded feeder neutral and/or the branch circuit neutral. In my mind, the theoretical junction point of the main bonding jumper splits the "neutral current" into "grounded service conductor current" and to other currents that are not really given names by the NEC. These other currents exist by the requirements of the NEC in all but the rarest of occupancies. In the Real World, the theoretical main bonding jumper point in the circuit has to include all the other conductive paths that happen when conductive materials, by mechanical assembly, form a complete path that current can travel along back to the Source (the PoCo transformer).
And, again, I repeat. I would benefit from your unpacking what "intended" means to you.
I would call it magical if the source is truly ungrounded.Here's a thought for you to ponder... Where a power source with a neutral point is permitted to be an ungrounded system (atypical of most, I know), what would you call any current from the power source returning to it on the grounding system?
The only place that this current you have just named exists is on a theoretical circuit diagram with resistance-less line conductors and a "point" of zero dimension as the Main Bonding Jumper (MJB), the node towards which all the branch and feeder neutral currents aggregate, and from which other currents leave. It is sloppy thinking to call the summed neutral currents in the theoretical point of the MJB as the same as the current in the Grounded Service Conductor in this context of "Test Question - Troubleshooting" and it's diagram.All unbalanced ungounded conductor current is neutral current.
And it is even sloppier thinking to say that the power of "intention" can overrule the Laws of Physics in the Real World and that the summed branch and feeder neutral current will, therefore, go only into the Grounded Service Conductor regardless of other current paths that return to the same source.It is intended that all the neutral current return on the neutral conductor.
:thumbsdown:I would call it magical if the source is truly ungrounded.
Quite true.:thumbsdown:
You know darn well the NEC does not consider reactive or magnetic coupling as a means of grounding.
I believe your reply exemplifies the root of our disagreement. There is no MBJ, grounded, or grounding conductor involved in a discussion about neutral current.The only place that this current you have just named exists is on a theoretical circuit diagram with resistance-less line conductors and a "point" of zero dimension as the Main Bonding Jumper (MJB), the node towards which all the branch and feeder neutral currents aggregate, and from which other currents leave. It is sloppy thinking to call the summed neutral currents in the theoretical point of the MJB as the same as the current in the Grounded Service Conductor in this context of "Test Question - Troubleshooting" and it's diagram. And it is even sloppier thinking to say that the power of "intention" can overrule the Laws of Physics in the Real World and that the summed branch and feeder neutral current will, therefore, go only into the Grounded Service Conductor regardless of other current paths that return to the same source.
You really need to explain what "intended" means to you. From my reading it seems almost mystical.
IF, between the MBJ and the source, there are two or more current paths, the current in the Grounded Service Conductor will NEVER equal "all unbalanced ungrounded conductor current", EXCEPT for when the unbalance current is Zero, and, therefore, the Grounded Service Conductor current is a different current than "all unbalanced ungrounded conductor current."
:thumbsup:Quite true.
In which case I would call any current returning to the source over the ground system "small".