Sparky2791
- Northeast, PA
- Electrical Design
I am having a friendly disagreement with a client regarding a ground wire requirement.
The utility company brings 13.2 KV to the exterior pad mounted transformer and customer pulls 480/277V into the building from the secondary side. I believe a separate ground wire is required to be pulled from the three phase pad mounted utility transformer to the switchgear as an equipment bonding jumper. System bonding happens inside at the switchgear. My client feels no ground is required to be pulled into the building only one tied from the transformer enclosure to the ground ring around the transformer so only a neutral wire is required into the building (other than the phase conductors).