230.82 Equipment Connected to the Supply Side of Service
Disconnect. Only the following equipment shall be
permitted to be connected to the supply side of the service
disconnecting means:
(1) Cable limiters or other current-limiting devices.
(2) Meters and meter sockets nominally rated not in excess
of 600 volts, provided all metal housings and service
enclosures are grounded in accordance with Part VII
and bonded in accordance with Part V of Article 250.
(3) Meter disconnect switches nominally rated not in excess
of 600 volts that have a short-circuit current rating
equal to or greater than the available short-circuit current,
provided all metal housings and service enclosures
are grounded in accordance with Part VII and
bonded in accordance with Part V of Article 250. A
meter disconnect switch shall be capable of interrupting
the load served.
(4) Instrument transformers (current and voltage), impedance
shunts, load management devices, surge arresters,
and Type 1 surge-protective devices.
(5) Taps used only to supply load management devices,
circuits for standby power systems, fire pump equipment,
and fire and sprinkler alarms, if provided with
service equipment and installed in accordance with requirements
for service-entrance conductors.
(6) Solar photovoltaic systems, fuel cell systems, or interconnected
electric power production sources.
(7) Control circuits for power-operable service disconnecting
means, if suitable overcurrent protection and disconnecting
means are provided.
(8) Ground-fault protection systems or Type 2 surgeprotective
devices, where installed as part of listed
equipment, if suitable overcurrent protection and disconnecting
means are provided.
(9) Connections used only to supply listed communications
equipment under the exclusive control of the serving
electric utility, if suitable overcurrent protection and
disconnecting means are provided. For installations of
equipment by the serving electric utility, a disconnecting
means is not required if the supply is installed as
part of a meter socket, such that access can only be
gained with the meter removed.