Penwar
- United States
Here I go, exposing my lack of history with 3-phase.....
for sizing the conductors and fuses for a disconnect:
1st time at this one, please be gentle.
208Y/3-PH/4-wire system. Connecting (6) inverters (solar) to an existing grid system. Output of each inverter is 25A. So a total of 150A*1.25 = 187.5. Utilizing a 3-ph panel with 2-pole breakers (figuring 35A breakers). Figuring that the current at each leg to be 62.5A. I am curious how I go about sizing the wires out of the panel and the final disconnect switch (200A). Do I size the wires based on the total load (187.5A), or do I size each of the 3-wires for the load from each leg off the panel (62.5A).
I am at a total loss on this. My gut tells me that I go for the entire load, which being in conduit, underground, 100' run would be 3/0 (with 1.37% drop). This is fine if correct, but why would it not be a #4 for each wire.
Along with this, for a 3-ph AC disconnect switch, would this be (3) 80A breakers, or (3) 200A breakers.
I believe I am missing something fundamentally.