I do not think it is relevant to the matter discussed here because if, in principle, the voltage drops across individual ground resistances are known, for example, across the GEC rod ground resistance and across the POCO's neutral ground resistance, the voltage drop across the neutral wire connecting the two resistances is the sum of these two voltage drops.The question asked earlier was about measuring, not calculating. And clamp injection devices for directly measuring individual earth resistances have been around for years. The techniques do, however, require the existence of a second earth access path to enable current flow, as well as access to a remote ground voltage reference.