Article 406.4(D)(2)(c) allows non-grounding type receptacles to be replaced with grounding type if supplied from a GFCI, breaker OR receptacle is my assumption as it does not state. An equipment grounding conductor shall not be connected between the grounding type receptacles as well.
The question I have is whether or not this practice is allowed where GFCI protection is actually required (kitchen) versus doing it in a family room or similar location. Essentially, I have a kitchen which is currently wired with 2 wire NM cable. Unfortunately, the framing on the exterior walls consists of furring strips on block walls with very shallow boxes. Not a location where I can fish new wires, replace the existing non-grounding receptacles individually with GFCI receptacles or even replace the existing boxes with deeper ones to accommodate GFCIs. My thought was to locate the hot and neutral for the receptacles in question and supply from a GFCI breaker and then replace the receptacles with grounding type.
Am I missing something or is this simple, yes, it's allowed? I rarely utilize this article.
The question I have is whether or not this practice is allowed where GFCI protection is actually required (kitchen) versus doing it in a family room or similar location. Essentially, I have a kitchen which is currently wired with 2 wire NM cable. Unfortunately, the framing on the exterior walls consists of furring strips on block walls with very shallow boxes. Not a location where I can fish new wires, replace the existing non-grounding receptacles individually with GFCI receptacles or even replace the existing boxes with deeper ones to accommodate GFCIs. My thought was to locate the hot and neutral for the receptacles in question and supply from a GFCI breaker and then replace the receptacles with grounding type.
Am I missing something or is this simple, yes, it's allowed? I rarely utilize this article.