Is a main breaker required for a subpanel if over-current protection is provided for feeder connectors
408.36 Overcurrent Protection. In addition to the re-
quirement of 408.30, a panelboard shall be protected by an
overcurrent protective device having a rating not greater
than that of the panelboard. This overcurrent protective de-
vice shall be located within or at any point on the supply
side of the panelboard.
hello! first post here.
For an example, if the main is outside rated at 200 amps. the cuductors are 2/0 going to a 100 amp sub panel directly from to 200 amp breaker. . is this not compliant?
hello! first post here.
For an example, if the main is outside rated at 200 amps. the cuductors are 2/0 going to a 100 amp sub panel directly from to 200 amp breaker. . is this not compliant?
That would not be compliant since the overcurrent protective device is larger than the rating of the panel.. 408.36
Dennis can correct me if I'm mistaken, but I believe that one possibility of such an installation being complaint would be if your 2/0 conductors met the tap rules in 240.21 and your subpanel had a 100 amp main to conform with 408.36 and 240.21
(the other "not likely" scenario would be the 2/0 are "whole house feeders" and the sub has a 100 amp main)
Is the 100 amp breaker at the source or in the sub panel?
I agree with Gus. Easiest fix would be install a 100 amp breaker at the main panel.