cdcengineer
So I have a project where we have some long branch circuit runs.  I don't recall the specifics, but let's assume that there are two 50A/2P, 208V receptacle circuits served from a 208Y/120V, 3-Phase, 4-wire service.  Both of these branch circuits share a common underground PVC conduit and the conductors were sized per 310.15(B)(3)(a), re: more than (3) ccc's.  For discussion purposes, let's say that the longer of the two is 475' and the shorter is 425'.  I believe they might be #2 AWG CU.
The local AHJ required that the circuits be protected by GFCI breakers. The circuits serve 50A receptacles that serve occasional event power via 50A spiders. I argued with the AHJ that the spiders have (6) 20A GFCI receptacles and that the GFI protection is redundant.
Anyway, the contractor tried to energize these circuits and when trying to heat both up, one would trip. I believe he said that if #1 was energized, than when he fired up #2 one would trip. Same goes for if he had #2 on and fired up #1. I'm not sure if it was one recep or the other. I will verify this tomorrow as it now seems to be a critical component as I write this.
He questioned whether there could be an induced voltage from the first circuit which was causing the GFI to trip. He stated that when they broke apart one of the circuits into individual conductors, they were able to read a voltage to ground from the hots (between 8 and 14 V). I don't believe they were reading any voltage when referencing the neutral (grounded) conductor. My first question was, "what type of meter are they using". A high impedance DMM might read ghost/phantom voltages. Whereas a low impedance tester like the T+ pro or Fluke 117 might not see any voltage. This should clear up quite a bit. My understanding is that with a low Z meter, if we see voltage, than there could be a back-fed or bleed voltage from another conductor. Considering that all the wires were broken apart, I would think that they can rule out back-feed. But because the wires are underground and it's not unusual to find water in conduits here at 10k feet above sea level, than perhaps compromised insulation is causing the voltage they are reading.
I don't believe unduced voltage is the culprit in this case. But perhaps the members can provide some of their own experiences on this topic. I initially thought that redundant GFI protection could be the culprit. However, after talking with a manufacturer, they said that that hasn't been a problem with newer generations of GFI for a long while.
I did some research on induced voltages, and I would not doubt that there could be an induced voltage at such long lengths and I'm betting that the wires are a twisted mess within the conduits. However I don't see that as possible with no loads plugged into the circuit. My thought is no current = no chance for induction. Although perhaps the length of the conductor (ie resistance) is acting as a load. However this should not cause a GFI brkr to trip. The breaker is looking for heat, overcurrent and current out = current in within 3 to 5mA.
Is it possible that an induced voltage with such long conductors (resulting in high resistance Z) is adding current to the circuit which when seen by the GFI is causing this?
I suggested they get the low Z meter and start there. If that shows no voltage than I would say the next simplest solution would be to look at the possibility of a bad breaker (or two). This scenario is one of at least a half dozen that were used at the same event, and there were no other problems. Therefore I though they might try swapping breakers with a known good GFI. If for some reason they see a voltage with the low Z meter, than it's gotta be a case of bad resistance. This could be found with a MEGGER.
As of right now, I am just trying to provide some helpful tips. And if anyone has some first hand experience with a situation similar to this, please feel free to provide insight.
As always, thanks.
As always, thanks.