gar
- Ann Arbor, Michigan
- EE
140920-1212 EDT
Some experiments:
Using a 250 ft coil of #14 romex with EGC. This was not uncoiled.
Capacitance @ 1 kHz:
0.0050 ufd D=0.22 --- Black to white with EGC floating
0.0066 ufd D=0.28 --- EGC to white with black floating
0.0072 ufd D=0.26 --- EGC to black with white floating
Voltage --- 10 Megohm input impedance:
0.019 V --- EGC to white residual with 47 ohm meter shunt
26 V --- EGC to white with 124 V from EGC to black, not easily predicted.
60 V --- EGC to white with 124 V from white to black, expected.
0.030 V --- EGC to white with 47 ohm meter shunt 124 V white to black
0.030 V --- EGC to white with 47 ohm meter shunt 124 V white to black and a 10 A load at the far end.
Note the secondary loop is about 1/2 the area of the primary loop.
0.03 V across 47 ohms is less than 1 mA. This is in the mud so we can not tell much, but it is not a large current.
I do not want to uncoil the loop and try to do a more controlled experiment.
Some experiments: