But if you daisy chain then it becomes a raceway and needs a strap
Not sure but guessing this is the same in 2014, here is what is in the 2014:art 330.30(D)(2)[nec '08] states if the cable feeding a luminaries is not over 6 feet it does not have to be supported. My question is if the same cable is terminated in a jbox in the accessible celling will it have to be supported with in 12 inches of the jbox 330.30 b .
How does it become a raceway? It is still a cable wiring method regardless or length or installation methods.No strap. But if you daisy chain then it becomes a raceway and needs a strap
I thought if it were from a j box and flexed down to the light and under 6' no strap was needed and mc / aluminum had to be strapped 12" from termination. Nothing can be laying on grid as means of support there for independant ceiling wires must be used connected at both ends not because its an electrical code but a bldg code. Ceiling grid manufacturer would have to sing off saying the grid is rated to hold the mc
Not per the NEC. Read all the 3XX.30 sections.
With that being said, local building codes may be another story and 410.36 may be of some interest too.
Roger
	I don't see what 300.11 has to do with a connector being used as a means of support. I will say in a situation where no other support means is necessary that kind of leaves the connector tasked with providing support to at least some extent.
I must have missed something. I didnt know a connector could be used as a means of support. But I thought what I said was the same as 300.11
Someone said my statement was not true by nec code and that 300.11 would help. Sorry if I misunderstoodI don't see what 300.11 has to do with a connector being used as a means of support. I will say in a situation where no other support means is necessary that kind of leaves the connector tasked with providing support to at least some extent.
300.11 does address supporting of wiring methods, but doesn't address connectors being allowed as the support method, yea or nay, and doesn't cover the six feet of unsupported methods allowed in specific instances. You have to read other sections to answer some of those questions.Someone said my statement was not true by nec code and that 300.11 would help. Sorry if I misunderstood