I have a building where we are working that has a Combination ATS Fire Pump Controller. The Generator has a dedicated breaker that protects the Emergency feeder to the ATS/Controller. The Normal Feed comes underground directly from the Utility Transformer to the ATS/Controller...there is no Disconnect/OCPD for these Service Conductors from the Utility Transformer....? I have never seen this before. This Fire Pump room is in the main building but it is only accessible from a door on the outside of the building, no access from inside, if this even makes a difference.
I am use to seeing a TAP inside of the Gear before the Main Disconnect going to the Fire Pump Room and landing on a Seperate Disconnect with OCPD for Short Circuit/Ground Fault Protection fused at the LRC rating of the Fire Pump. There literally is no OCPD for this Fire Pump. Am I missing something? I have read 695 and cannot find anything to support not having protection on these conductors for Short Circuits/Ground Faults.
This is an Engineered Job with stamped drawings. Any ideas? :?