No OCPD, connected directly to the service transformer - yep.
I was involve in repairing a fire pump feeder - mid 1990s. Parallel 250kcil, maybe 750 feet, 3" rsc, 3' burial, concrete incased. Fault developed in the middle of one of the 3" rsc.
Service was 480 grnd Y, 750kva, utility owned oil filled pad mount, ug 34kv primary fed from pole outside the plant, xfm located inside the plant ~75" from the outdoor serviceequipment.
Showed up in the morning to bad electrical - looked like one or two phases out.
Called the power company, they came out and replaced the transformer 34kV primary bayonet fuses. They don't have the 10A fuses so they use 30A. Lineman turns switch on the xfm. Transformer starts rumble, smoke starts coming out of the service equipment. Lineman drops the pole he is holding for the xfm switch actuation. Runs over to truck, parked out by the pole, jumps in the bucket, goes up and jerks the cutouts open.
It was obvious which conduit had the fault. The locknuts were burned off, melted. The wire insulation from that conduit was bubbled, scorched.
Connected a boom truck to the conductors at the fire pump end and pulled until we tore them off. Pull the other end till we tore it off. Laid the conductors on the ground over the conduit path. We dug up the conduits where the 6' section was missing. Yep - burned and melted right clear though the conduit. Concrete and 2" minus backfill looked like it was trying to turn into glass.
I have no clue as to how/why the cable decided to fault after 5 years in service, in the middle of the run, in conduit, concrete incased. No backhoes, no water, didn't see any rocks in the conduit when I pulled out the wires. No obvious nicks in the insulation - at least none that I could tell were there before we pull them out with a boom truck. :?
So I am asking the fire marshal, How about we install a mag only CB for the fire pump feeder? I offered a 1200A frame, 4000A instantaneous only. In 30 years there had never been a fire that threatened the plant. The fire pump feeder failure could have taken out the whole place. I don't know where the electrical would have burned clear had the lineman not pulled the pole cutouts - I suspect when the xfm blew up
Fire Marshal said No. No OCP between the service and the fire pump controller. He absolutely understood the NEC allowed appropriatle sized OCP.
I'm still baffled as to the cause. But I think the Fire Marshal considered the failure a way-the-hell-out-there-fluke.
I'm not saying the fire marshal is wrong ..... but ....... Nah, no buts. I'm not saying he was wrong
ice