Here's what I currently have put together for a proposed revision:
Comments...
Only a problem with some... yes, perhaps most.Yes, that is always a problem when using free software from the internet.
It is not "unknown" software. If you researched it, you would discover the details. IIRC, it is based on the empirical data from a study sponsored by IAEI. It is compiled by a team of students under the tutelage of the same professor that supervised the study, I think... too many hours on the road to have total recall at this point... so I'll leave it to you to uncover any error...Usng an unknown free internet software with no defined algolrithm does not sound like a good idea to me. I can only hope the CP would not pick a specific software.
However, if the algolrithm were published in a peer reviewed IEEE paper, then the proposal could read like 310.15.C.
... It is not "unknown" software. If you researched it, you would discover the details. IIRC, it is based on the empirical data from a study sponsored by IAEI. It is compiled by a team of students under the tutelage of the same professor that supervised the study, ...
You make a good point. So the question remains how to present the proposal so the CMP will accept or accept in principle. As I noted earlier, if a simple exception for engineering supervision, we have no guarantee of the algorithm used, not to mention it precludes non-engineers. What if we state something on the order of software developed for the purpose and approved by the authority having jurisdiction... then mention the GEMI software by way of an informational note. AFAIK, it is the only software which is designed to perform this analysis. Are there any others?And I'm certain they did a fantastic job. However, until the algolrithm is published and peer reviewed - it is unknown. Quien Sabe. Maybe the iaei journal is considered peer reviewed. And the article they published is considered sufficient - I wouldn't think so, but maybe it is.
The other issue is the NEC never picks a specific software to use. Rather they will pick an algorithm. Article 310.15.C is an example. What ever software might be chosed is a design decision.
I would never ascribe to me sufficient understanding to even offer a guess as to an NEC code panel actions. However, I can only hope they would not pick a specific software.
All this aside (so seriously): You care. You're making a good faith effort to help out and clear up a nebulous section. I am absolutely in favor of your efforts - and impressed.:thumbsup: It's way more than I could do.
ice
Right on both counts. Generally speaking, if one wishes to do engineering for hire - get a PE ticket.... if a simple exception for engineering supervision, we have no guarantee of the algorithm used, not to mention it precludes non-engineers. ...
Repeated from previous posts:... What if we state something on the order of software developed for the purpose and approved by the authority having jurisdiction... then mention the GEMI software by way of an informational note...
First, that's why I said mention GEMI in an Informational Note. IMO, GEMI isn't a specific brand. Something has to be commercialized in some manner before it is a brand. In fact, IEEE, ANSI, NFPA, UL, etc. are closer to being brands than is GEMI. And like I said, I don't know of any other software designed for the purpose. Do you?Right on both counts. Generally speaking, if one wishes to do engineering for hire - get a PE ticket.
Why is it mandatory to use software? Why can't one use paper, pencil, and an abacus? No other similar code sections post anything except the algolrithm. The method of compliance is a design decision. The code never mentions specific name brand software. The closest they get is to mention other engineering standards, API, NFPA, ANSI, IEEE, even UL - but never a specific brand
How do we know that it works? Any single source of information that was paid for by an organization with a vested economic interest in the outcome is always a bit suspect..... Ultimately, it comes down to, if it works, why knock it. Seems to me you are just looking for such a reason.
But the information on how the Neher-McGraph calculations is out there and has been reviewed. As far as how you do the actual calculation is not as important as how or if the calculation actually works.As to why use software instead of paper and pencil... it's time to get your time frame into the 21st century. We are not going to go backwards. And as Bob mentioned, it is a complex calculation. I'm guessing it's on par with Neher-McGrath calc's. So tell me what percentage of engineers performing those calc's resort to using paper and pencil vs. software...???
I agree to a degree. But I ask you, having made that statement, who stands to benefit economically? I also see what appears to be much less substantiation went into the current Code requirement. Granted, I have not been made privy to discussions that CMP's may have had on the matter. All I see is what started it, and what the end result is.How do we know that it works? Any single source of information that was paid for by an organization with a vested economic interest in the outcome is always a bit suspect.
I'm certain I am biased. When I was getting started, maybe 40 years ago, state law discussed "product of engineering" and "engineering for hire". If one wishes to do those things, then the state requires getting a PE ticket. The law has not changed much in the last 40 years. And what you are advocating certainly appears to be "product of engineering" - the same as any other similar section (allowing calculaton using an accepted algolrithm)... As far as published and peer reviewed, or even practicing what may appear as an engineering task, I believe you are a bit biased being an engineer yourself. ...
... As to why use software instead of paper and pencil... it's time to get your time frame into the 21st century. We are not going to go backwards. And as Bob mentioned, it is a complex calculation. ...
IMO:.... We are not going to go backwards. ....
Well, you hit the key word, you're guessing. And that is because ..... (drum roll)...And as Bob mentioned, it is a complex calculation. I'm guessing it's on par with Neher-McGrath calc's. So tell me what percentage of engineers performing those calc's resort to using paper and pencil vs. software...???
The Steel Tube Institute sponsored the work that led to the GEMI software. I think that the main focus of the project was not on the fault clearing path, the more on the ability of steel conduit to provide shielding to sensitive circuits.I agree to a degree. But I ask you, having made that statement, who stands to benefit economically? I also see what appears to be much less substantiation went into the current Code requirement. Granted, I have not been made privy to discussions that CMP's may have had on the matter. All I see is what started it, and what the end result is.
As I understand on review, it was NEMA that sponsored the study....The Steel Tube Institute sponsored the work that led to the GEMI software. I think that the main focus of the project was not on the fault clearing path, the more on the ability of steel conduit to provide shielding to sensitive circuits.
Well let's get down to the nuts and bolts of the issue. Using any wire-type EGC size between Table 250.122 size and upsized proportionately with upsize in ungrounded conductor (i.e. an excepted size) to be determinable by the lay person. Short of that, I will not be submitting a proposal. Feel free to submit an proposal for exception under engineering supervision yourself.... :happyyes:I'm certain I am biased. When I was getting started, maybe 40 years ago, state law discussed "product of engineering" and "engineering for hire". If one wishes to do those things, then the state requires getting a PE ticket. The law has not changed much in the last 40 years. And what you are advocating certainly appears to be "product of engineering" - the same as any other similar section (allowing calculaton using an accepted algolrithm)
Hummm... So you think I should give up my steam powered sliderule - NEVER
Yes there are reasons that one might not use software. For example: I have ETAP available on my computer. I get asked regularly about some specific arcflash. Now, I can set up an ETAP model and let the computer calculate. Takes me a few hours. Or I can take the equations right out of IEEE 1584, use pen and calculator and be done in 1/2 hour.
Another example: Supose one needs a single phase Short Circuit Current. I don't even know how to setup an ETAP model for this. However, I can use the Busmann point to point, and be done in an hour.
Of course, my coal fired calculator uses RPN which automatically makes me significantly faster than any of the parentheses machines.
And another - not exactly on point, but still: Show me a spreadsheet that can do complex math (3ph circuit analysis). Program it for a polar- rectangular swap. One can do it but it is a mess. Now add complex matrix math. (transmission lines) Spreadsheet-yuck. My 20 year old calculator - yep, it will do these and relatively cleanly.
All this required one understands the physics. No way to do this if the algolrithm is not published.
IMO:
Understanding the physics is not going backwards.
Depending on canned software with out knowing the physics, is worse than going backwards.
It is not published.
Not just resistance of the fault path, but resistance/impedance in the entire circuit (including source impedance) during the fault is what determines how much current will flowI agree that in many cases it over does the upsizing of the EGC to an unnecessary size, but as I have seen in many other threads posted on this subject no one has come up with a better way of doing it that would be accepted by the code panel, the idea of a chart is a good one but it would be unbarring large to cover all the lengths up to lets say 1'000 feet runs for every size conductor, since it is not based directly upon the circuit size and more based upon the resistance of the fault path.
250.4(A)(5) Effective Ground-Fault Current Path. Electrical
equipment and wiring and other electrically conductive material
likely to become energized shall be installed in a
manner that creates a low-impedance circuit facilitating the
operation of the overcurrent device or ground detector for
high-impedance grounded systems. It shall be capable of
safely carrying the maximum ground-fault current likely to
be imposed on it from any point on the wiring system
where a ground fault may occur to the electrical supply
source. The earth shall not be considered as an effective
ground-fault current path.
I can relate to this. I'm currently working 6/12's on nights. One advantage is I can squeeze off a post here and there while I'm at work (but obviously not working...
I'm sure we could add to this list but after working two doubles in a row it's a little hard to get the ol mind to work any harder right now.